I'm building a bathroom on the first floor for my mother. Since this is at the far side of the house I have to run a 3" line over to the nearest vertical stack which is 23' away.
My problem is that for the first 7ft I must stay below a height of 55" and for the remaining 16ft I must be below a height of 36"
The tie in to the vertical stack is at a height of about 24"
By my calculations using a min 1/4" per ft slope my line should be at least 8" higher on the high side,right?
Is the best way to do this in one straight shot or should I run the first 7ft with 1/4" slope then vertical drop or 2 45s to get the last 16ft at 1/4" slope at the lower height?
I'll try and get a pic posted but I'm on my blackberry right now.
Thks
Rem