I am confused by the following:
- On one hand code (IPC) clearly states that " 905.4 Vertical rise of vent. Every dry vent shall rise vertically to a point not less than 6 inches (152 mm) above the flood level rim of the highest trap or trapped fixture being vented. " It even has the following diagrams showing acceptable vs unacceptable:
Yet below is a diagram with the vent line connecting to drain line with a wye angled at 45 (ok, that's vertical, not horizontal per code) followed by a section sloped at 1/4in per foot (clearly << 45 deg, so not vertical?), and clearly under the flood rim of the toilet.
With the following comment: "When a branch drain must travel through a floor platform before reaching a stack, the drain must slope gradually. Here, the angle the vent takes off from the toilet drain is critical—it must not be less than 45°, as depicted in the cross-section drawing on the facing page."
So my question is: Is that diagram a fail code wise? ( I've also seen other similar diagrams from other sources claiming that's ok.) Or is the 45 deg orientation of the wye from horizontal, which would end up higher than the top of the drain pipe, enough? And if this is code, is there a limitation in length (as long as you can maintain the 1/4in /foot slope) between the two 90 deg elbows?
Confused ... thank you in advance for any comments.
- On one hand code (IPC) clearly states that " 905.4 Vertical rise of vent. Every dry vent shall rise vertically to a point not less than 6 inches (152 mm) above the flood level rim of the highest trap or trapped fixture being vented. " It even has the following diagrams showing acceptable vs unacceptable:
I am also well aware of many posts here and elsewhere pretty much saying "No flat vent below flood rim, period" ... sloped or not, etc ...Yet below is a diagram with the vent line connecting to drain line with a wye angled at 45 (ok, that's vertical, not horizontal per code) followed by a section sloped at 1/4in per foot (clearly << 45 deg, so not vertical?), and clearly under the flood rim of the toilet.
With the following comment: "When a branch drain must travel through a floor platform before reaching a stack, the drain must slope gradually. Here, the angle the vent takes off from the toilet drain is critical—it must not be less than 45°, as depicted in the cross-section drawing on the facing page."
So my question is: Is that diagram a fail code wise? ( I've also seen other similar diagrams from other sources claiming that's ok.) Or is the 45 deg orientation of the wye from horizontal, which would end up higher than the top of the drain pipe, enough? And if this is code, is there a limitation in length (as long as you can maintain the 1/4in /foot slope) between the two 90 deg elbows?
Confused ... thank you in advance for any comments.