Wet Venting confusion
Spoolofpipe
Austin, TX
We are in a odd situation, we are under IPC 2015 and the inspector is not signing off on our design
The system is designed like this
4" sanitary line out < 4x4x3 Combination Wye-1/8 bend < toilet
3" common drain (horizontal wet vent for toilet) that serves 2 sinks, washer, and a shower
the sinks, washer and shower all dry vent out of the common stack
only the toilet is wet vented through the 3" drain/vent, our MEP engineer says its good, our Code guy says its good, QA says its good, but the inspector does not agree
Thoughts?
Spoolofpipe
Austin, TX
its very similar to this:
except instead there is no floor drain and the bathtub is a washing machine drain and the leg from the toilet to the main line is 4" and the entire common drain and vent stack are 3"
The washer is doing it to you. That needs to wye in downstream of the toilet if you want to wet vent the toilet by the lavs and shower.
The washer isn't considered part of the the bathroom group for wet venting.
Or you can add a vent for the toilet.
Spoolofpipe
Austin, TX
Thanks Terry, I appreciate it, Definitely going to vent the washer downstream of the toilet, that will be much easier to rework
just in case, I have read that part of the IPC like 30 times, where would it say that about the washer?
Spoolofpipe
Austin, TX
Section 909 on wet venting for bathroom groups.
https://www2.iccsafe.org/states/Puerto_Rico/English_Codes/IPC English/PDFs/Chapter 9.pdf
The washer isn't part of that. It's a pumped fixture.
The inspector also might not like the unwashed 3" near the lav. Is there a cleanout there?
so another thing I just realized, the sink on the far side of that wet wall is for a kitchen, so that means I need to move it out of the wet vent line for the toilet correct?
what do you mean by unwashed 3"?
we hadnt installed any cleanouts as we were relying on the washer drain as the "removable fixture" to snake through
Spoolofpipe
Austin, TX
Can you wet vent the clothes washing machine through the non-bathroom sink on the other side of the wet wall?
Wet venting is allowed for bathroom groups on the same floor.
The non bathroom sink needs a vent, and the washer needs a vent. Those can tie in downstream of a bathroom that uses wet venting.
Or, vent everything.
Spoolofpipe
Austin, TX
ok thank you
Spoolofpipe
Austin, TX
connecting the shower to the 3" vertical vent would correct the "unwashed" 3" section.
thanks
I ended up moving the washer and kitchen sink over to an independent drain and put the lav sink in the 3" vertical vent, so the bathroom (WC, shower and lav) are on a wet vent circuit