We are in a odd situation, we are under IPC 2015 and the inspector is not signing off on our design
The system is designed like this
4" sanitary line out < 4x4x3 Combination Wye-1/8 bend < toilet
3" common drain (horizontal wet vent for toilet) that serves 2 sinks, washer, and a shower
the sinks, washer and shower all dry vent out of the common stack
only the toilet is wet vented through the 3" drain/vent, our MEP engineer says its good, our Code guy says its good, QA says its good, but the inspector does not agree
Thoughts?
The system is designed like this
4" sanitary line out < 4x4x3 Combination Wye-1/8 bend < toilet
3" common drain (horizontal wet vent for toilet) that serves 2 sinks, washer, and a shower
the sinks, washer and shower all dry vent out of the common stack
only the toilet is wet vented through the 3" drain/vent, our MEP engineer says its good, our Code guy says its good, QA says its good, but the inspector does not agree
Thoughts?