Let me get something straight. Can you actually run indoor wire underground if it's covered by conduit? I was looking at the depth codes and it shows "direct burial" cables but also has conduit depths.

Like metal conduit it says 6" ? PVC is 18 "

Can you actually run steel conduit underground ?

Anyway -- the main question is whether you can use indoor cable in underground conduit. THANKS.
 

Bluebinky

Member
Messages
588
Reaction score
16
Points
18
Location
Des Moines, WA
Let me get something straight. Can you actually run indoor wire underground if it's covered by conduit? I was looking at the depth codes and it shows "direct burial" cables but also has conduit depths.
No, "indoor" wire cannot be run underground, even in conduit. Conduit fills up with water.
 

Mar3232

Member
Messages
246
Reaction score
2
Points
18
Location
Indiana
That's what I thought. What do they mean when metal conduit only needs to be buried 6" deep? (or at least something I saw said that).

Regular steel conduit ? Something special ? I think it's galvanized but I would think the regular stuff would corrode bad over time.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
Code says rigid metal conduit or intermediate metal conduit, not EMT for the 6" depth. I guess it depends on the type of dirt and water table but they seem to hold up OK.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The depth requirement is to prevent damage to the pipe if you are using something like a RotoTiller which WOULD chop PVC conduit so you have to bury it deeper than the RotoTiller can dig.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
There is a big difference between EMT and rigid conduit. Rigid is approved for burial when used with the appropriate fittings.
THWN rated wire is approved for use in conduit, indoors or out.
 