pipe size /max length of run for kitchen, Canada Code

Discussion in 'Canadian Plumbing Code Questions' started by Philbert, Aug 7, 2010.

  1. Philbert

    Philbert New Member

    Joined:
    Aug 7, 2010
    Location:
    Toronto,Ontario,Canada
    hello
    I have been asked to rough in a new kitchen, it has 1 double sink and a dishwasher beside it, the soil pipe is 25 to 30 feet away, I don't want to run 3 inch all the way if it isnt needed , thanks
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    Even IF 1 1/2" would be approved, there is no way I would EVER use it for anything other than a vent. I ALWAYS use 2" minimum for my drain lines.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Philbert

    Philbert New Member

    Joined:
    Aug 7, 2010
    Location:
    Toronto,Ontario,Canada
    the problem I am having is that if I seach online for a quote from the npc I get a vague reference to some "complicated table" in the plumbing code book which I can acces online unless I pay for it or order a copy of the code book for a price of course,if ther is no restriction all the better, although I will likely use 2 inch anyways, ohhh the 25 to 30 foot run is a sloped run not a drop ifin that changes anything
     
  5. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego, CA
    It is not a "complicated table" at least not in the books down here. Each fixture is desinated by a number which correlates to how much water is likely to go in it. The number is called "fixture units". In the UPC, a kitchen sink is 2 FU. By the simple table, the maximum # of FU on a horizontal 1½" pipe, beyond the trap arm, is ONE. So the sink needs to drain into a 2" lateral. The horizontal length ( with 1/4" per foot slope minimum) is unlimited.
     
  6. Doherty Plumbing

    Doherty Plumbing Journeyman & Gas Fitter

    Joined:
    Jun 22, 2009
    Occupation:
    Red Seal Journeyman Plumber & Licensed Gas Fitter
    Location:
    Penticton, BC
    1.5" is perfectly acceptable as long as you pick up your vent within 6'.

    I usually have a 1.5" fixture drain picked up by a 2x1.5x1.5" tee.
     
  7. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    I haven't seen 1.5 for kitchens since the 50's in the lower 48, not Canada though.

    Here we use a 2" waste line until the vent, and then a 1.5" trap arm. we are allowed 42" for the 1-1/2" trap arm.

    I guess the Canadian code for kitchen plumbing is pretty weak.
     
    Last edited: Jun 29, 2013
  8. Plumber1979

    Plumber1979 Certified Plumber

    Joined:
    Jul 15, 2012
    Occupation:
    Certified Plumber
    Location:
    Ontario
    im a plumber here in Ontario and its just fine to use 1 1/2 on a kitchen and it 5' for the vent
     
  9. mikeplummer

    mikeplummer Plumber

    Joined:
    Mar 28, 2012
    Location:
    Ontario, Canada
    1-1/2" is fine. trap arm max is 5' (1.5m). cleanout required on fixture drain or union p-trap. cleanouts every 20' (6m).. you'll want to make sure your slope is right to keep a kitchen sink line that long, clear of grease etc.
    secondly NPC is not what you need. you need to refer to the Ontario Building Code section 7 - Plumbing
     
  10. Sean Beck

    Sean Beck Plumber

    Joined:
    Jun 14, 2013
    Occupation:
    Plumber
    Location:
    Toronto, Ontario, Canada
    1.5" is permitted by code providing the vent is connected within 5ft and there is a clean out every 6m. Personally with it being a kitchen drain which is subject to grease build up, I would use 2" with cleanout every 6m.
     
  11. mikeplummer

    mikeplummer Plumber

    Joined:
    Mar 28, 2012
    Location:
    Ontario, Canada
    your posts suggest that your reply to the request of the customer should have been " I don't know plumbing - perhaps you should consult a plumber "
     
  12. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    pipe

    The code is a "minimum standard", and I do not know any "competent" plumber who has ever had to snake a sink drain who would use less than 2". With 3" you run into the problem of NO "self scouring" because the velocity is too slow. Use 2"!!!!!!
     
Similar Threads: pipe size
Forum Title Date
Canadian Plumbing Code Questions Vent pipe size - Alberta Jan 9, 2015
Canadian Plumbing Code Questions Minimum drain pipe size for a lav Mar 31, 2013
Canadian Plumbing Code Questions I need to know the vent size for a 2 inch shower pipe drain Oct 7, 2010
Canadian Plumbing Code Questions White capped pipe (4.5 inches) in a basement floor, what it is for ? May 1, 2017
Canadian Plumbing Code Questions Washer Standpipe and Laundry Sink Drainage Reconfiguration Jan 14, 2017

Share This Page