How many bends can be in a tub drain?

Users who are viewing this thread

Bena2048

New Member
Messages
4
Reaction score
0
Points
1
Location
Michigan
Im getting ready to run the drain for my basement bathroom but I'm concerned that I have too many turns in the tub drain. I had to start in the wrong direction in order to pick up a wall for a vent. Is this a problem, does it meet code? A second set of eyes on this would really be appreciated.
 

Attachments

  • Plumbing layout.jpg
    Plumbing layout.jpg
    30.9 KB · Views: 422

Kreemoweet

In the Trades
Messages
757
Reaction score
67
Points
28
Location
Seattle. WA
Which code? There are many! Under an old UPC rule, a trap arm less than 3" cannot have more than 90 degrees of direction
change without a c/o. Larger ones can do up to 135 degrees. The code that prevails in your location might be more liberal.
Code-compliant or not, it may not be a "problem".
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks