Thanks everybody for the information and comments in this forum—it's a very valuable resource!

I bought a house and after several months found a few leaks and some smells. Long story short, the drain system has open abandoned drain and vent lines in the crawl space and leaks in a handful of places. Lots of mixed materials from different generations of work. Plumbers that quoted a fix had a good laugh. Quoted me $10k for the job, which might be fair, but is way more than I can afford. The house is small—1 bath and 1 kitchen sink on one floor—so I think I can tackle this myself and have been reading up on code. Maybe one of you who has more experience can validate?

See attached sketch for my overall plan.

A few specific questions:
1. In the main drain stack down to the septic, there is currently one wye and one double fixture fitting. I think by code I can use two stacked 3x2x2 double sanitary tees here, which will help me route everything in the tight space. Is that right?

2. The toilet is only offset from the stack a couple inches, with two 3" 22.5 degree bends. Total length from flange to top of the stack is only about 12-18 inches. Is it permissible to vent this to the roof with one of the ports on the top sanitary tee? I think this is ok but this seems to be a pretty rare configuration so I'm having a hard time confirming.

3. With 2" pipe, I think I have to vent the tub before it gets to the stack, or the trap arm will be too long (10 feet). It fits in well to do this at about 2' from the trap, though I think I can go up to 4'. Any concerns?

4. As far as I can tell, the lav is currently not vented. Rather than open the whole wall to add a dry vent I was hoping to just add an air admittance valve in the cabinet below the sink. This Old House did this on Youtube, but I'm having a hard time determining if this is permissible in Washington. Thoughts?

5. Where would you want cleanouts in this system? By code I think I need cleanouts at the kitchen sink and after the second turn in its long run. Also need to get one in somehow at the main drain stack (I haven't figured out how to do this yet, but any solution there covers the toilet because of the short, straight drop). It's less clear to me if I need one for the tub/shower (total length will be about 12 ft).

6. Am I missing anything else?

Thanks all in advance. I appreciate your help and generosity!
 

Attachments

  • IMG_0080.PNG
    IMG_0080.PNG
    234 KB · Views: 142
Last edited:

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,473
Points
113
Location
92346
crude drawing but lav needs a vent, toilet cant be vented that way either unless the dry ventr connections are 6 inches above the bath tub and w/c again its crude drawing and maybe its not clear. kitchen is ok
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
All the vents need to be vertical until they are above the fixture they serve. Usually it's easier to go straight up and connect them in the attic.
 

dsandy

New Member
Messages
2
Reaction score
0
Points
1
Location
Washington State
Jeff and John, thanks for the help. I'm dealing with a pretty old house here, and so I'm trying to figure out how to work with what's here. None of the bathroom fixtures have a vent that is continuous with the drain—the vent through the roof is just off on its own and goes straight from roof to crawlspace before connecting to the system horizontally.

So I don't know how to wet vent in this situation, because none of the fixtures is vented without a horiziontal run. And the drain pipe to the septic is directly below the toilet with lav and tub on either side of the toilet, so the normal vent to drain arrangement is not possible.

To add dry vents I would have to open up at least two walls to add vent pipes and join them in the attic. The plumbers who estimated the job did not plan to open any walls (who knows what they were planning).

Is there any way to make this work in the crawl space given my constraints? This house is already a financial disaster, so I'd prefer to not add a bathroom tear out to the list.
 

John Gayewski

In the Trades
Messages
4,769
Reaction score
1,531
Points
113
Location
Iowa
You shouldn't need to tear out a whole wall maybe a patch.

Sorry I don't have any ideas for you other than to be creative and that snaking pvc through holes is possible as long as they are in the right spot.
 

Jeff H Young

In the Trades
Messages
9,792
Reaction score
2,473
Points
113
Location
92346
Its really hard to make suggestions based on the drawing there probebly are legal ways to plumb it but I dont know what you are willing to do . the lav vent is only part of the issue tub and toilet vents dont work either
 