Lightningwill
New Member
I was pretty sure I had a plan, but some tricky framing got in the way. Basically, for my master bath DWV, I can't land everything in the 9 1/2" joists in the way previously planned due to constraints on where I can drill some of the engineered lumber.
So I did some more brainstorming today and I'm pretty sure I have a solution (shown below). The biggest change vs. my previous idea is that the shower trap arm is now dry vented via a sanitee at the far end of the room (trap arm length is within spec). That sanitee drops directly into a 3" x 3" x 2" wye. The 3" input to the wye is a toilet drain.
The Question: Given that they both tie directly into an upright wye, is the vent on the shower sanitee adequate venting for the toilet as well?
Here's the relevant portion (12.8.4) of the 2015 NSPC: “For water closets and other fixtures that operate by siphonic action, the distance between the outlet of the fixture and its vent connection shall not exceed 3 feet vertically and 9 feet horizontally.”
If not, I'll upsize the lav drain to 2" to make it a wet vent, since it's too long if it's 1.5". But, I'd prefer to leave it at 1.5" if possible.
So I did some more brainstorming today and I'm pretty sure I have a solution (shown below). The biggest change vs. my previous idea is that the shower trap arm is now dry vented via a sanitee at the far end of the room (trap arm length is within spec). That sanitee drops directly into a 3" x 3" x 2" wye. The 3" input to the wye is a toilet drain.
The Question: Given that they both tie directly into an upright wye, is the vent on the shower sanitee adequate venting for the toilet as well?
Here's the relevant portion (12.8.4) of the 2015 NSPC: “For water closets and other fixtures that operate by siphonic action, the distance between the outlet of the fixture and its vent connection shall not exceed 3 feet vertically and 9 feet horizontally.”
If not, I'll upsize the lav drain to 2" to make it a wet vent, since it's too long if it's 1.5". But, I'd prefer to leave it at 1.5" if possible.