The attached is a photo of a proposed plumbing layout underneath a shower.

I’d like to pull a short run of horizontal vent off the pictured san tee, attaching a 90 directly on top of it and tying it into an existing vertical vent about a foot away. After the san tee, the drain line quickly drops below the weir, so this is why I’m needing to put the vent take off so close.

Any concerns with this set up?

Thanks very much for your advice.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
I'm not a fan of the vent fitting above the p-trap. Should be a medium 90 and not a vent 90.
Most codes require a wye or combo fitting if you pulling a vent off the horizontal now.
 

Girafdaniels

Member
Messages
49
Reaction score
4
Points
8
Location
KC
I'm not a fan of the vent fitting above the p-trap. Should be a medium 90 and not a vent 90.
Most codes require a wye or combo fitting if you pulling a vent off the horizontal now.

Thank you for the insight. I’ll steer clear of the vent 90 and do a combo.
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
Depending on the location of the vent pipe you need to connect to, a wye and two smaller bends could work and would be less total bend than a combo and a medium 90. Up to 6" above the shower flood rim, the vent needs to be plumbed as a drain. And it's supposed to stay vertical (meaning up to 45 degrees off true vertical) if possible.

Cheers, Wayne
 

Girafdaniels

Member
Messages
49
Reaction score
4
Points
8
Location
KC
Depending on the location of the vent pipe you need to connect to, a wye and two smaller bends could work and would be less total bend than a combo and a medium 90. Up to 6" above the shower flood rim, the vent needs to be plumbed as a drain. And it's supposed to stay vertical (meaning up to 45 degrees off true vertical) if possible.

Cheers, Wayne

Thank you, Wayne. Could work well that way and the drain line consideration is appreciated.
 