    So I have a 1.5” slip connection on one side and would love to connect it to a 2” female threaded. Space is super tight so ideally looking to do it in a single adapter but can use two provided they are low profile, any ideas?

    E0C11DB8-BA5E-45B8-BC42-FD88AA4FFA45.jpeg 585C2BB2-F38C-4585-A277-1BFBF0A02BDD.jpeg
     
  2. wwhitney

    wwhitney Well-Known Member

    Joined:
    Mar 17, 2019
    Location:
    Berkeley, CA
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
  5. Baltik

    Baltik New Member

    Joined:
    Apr 25, 2021
    Location:
    SF
  6. Baltik

    Baltik New Member

    Joined:
    Apr 25, 2021
    Location:
    SF
    That looks promising but I think wrong material - won’t glue with abs/pvc
     
    MASTERPLUMB777 likes this.
  7. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    With threads, yes.
     
    MASTERPLUMB777 likes this.
  8. wwhitney

    wwhitney Well-Known Member

    Joined:
    Mar 17, 2019
    Location:
    Berkeley, CA
    Sorry, both ends are threaded, why would you use any glue on this part?

    Cheers, Wayne
     
    Baltik likes this.
  9. Baltik

    Baltik New Member

    Joined:
    Apr 25, 2021
    Location:
    SF
    I’m not thinking straight, lol. Is stainless ok in a dwv application or will it eventually rust through?
     
  10. Tuttles Revenge

    Tuttles Revenge In the Trades

    Joined:
    Oct 15, 2014
    What is wrong with the threaded adapter Wayne first proposed? looks like a single fitting.

    What is that gray fitting anyway? Some form of trap?
     
    MASTERPLUMB777 likes this.
  11. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    I am not a pro. I expect stainless is good for DWV.

    The reducing nipple may be the better choice. Put washer and nut on that. https://www.homedepot.com/p/Everbil...with-Rubber-Reducing-Washers-C2698C/205154062


    https://www.zoro.com/zoro-select-2-x-1-12-mnpt-reducing-nipple-sch-80-rn200-150/i/G3452626/
    https://www.sprayerdepot.com/products/2-x-1-1-2-poly-reducing-nipple

    One concern is if the 1.5 inch slip joint pipe would fit into the schedule 80 1.5 side. Schedule 80 pvc pipe average ID is 1.500. Using a 1.25 inch trap would remove that concern.
     
    Last edited: May 7, 2021
    MASTERPLUMB777 likes this.
  12. Stuff

    Stuff Well-Known Member

    Joined:
    Mar 7, 2013
    Location:
    Pennsylvania
    Please provide an overview of what the job is.

    Assume you are trying to connect the white tailpiece to the black ABS drain behind it with a trap?
     
    MASTERPLUMB777 likes this.
  13. Baltik

    Baltik New Member

    Joined:
    Apr 25, 2021
    Location:
    SF
  14. wwhitney

    wwhitney Well-Known Member

    Joined:
    Mar 17, 2019
    Location:
    Berkeley, CA
    The plumbing code requires the trap to have a minimum 2" seal depth. That's the height of water from the top of the lowest cross section to the trap weir, aka the bottom of the outlet of the trap.

    Not sure what type of equipment that part is designed for, but if it doesn't have a 2" trap seal depth, you can't use it for a bathtub trap.

    For a 1-1/2" pipe, a regular solvent weld trap comes within 1/2" of the minimum possible height that complies with the trap seal depth requirement. Maybe with an unusual cross section at the bottom of the trap you could squeeze another 1/2" out of it. So the most you are going to gain with something non-standard that still complies with the plumbing code is 1".

    Cheers, Wayne
     
  15. Stuff

    Stuff Well-Known Member

    Joined:
    Mar 7, 2013
    Location:
    Pennsylvania
    That trap is designed to be part of a fixture, not part of the house drain system. It and others like it are not designed to be snaked so they need to be accessible to be removed when a clog occurs.

    How far are you from the wall? A bulkhead or tray ceiling might be needed. A creative 45º elbow on the end of the tailpiece could get it closer to the wall.
     
  16. Mr tee

    Mr tee In the Trades

    Joined:
    May 3, 2020
    Location:
    Montana
    If the SJ nut is going to end up in a concealed location it would not meet the UPC and you should use a solvent weld trap rather than one with a union.
     
    MASTERPLUMB777 likes this.
  17. Tuttles Revenge

    Tuttles Revenge In the Trades

    Joined:
    Oct 15, 2014
    Looking up some weird shower for a customer, Hansgrohe makes the perfect trap for this.. probably not legal or findable in the US, but it exists.

    [​IMG]
     
    MASTERPLUMB777 likes this.
  18. Baltik

    Baltik New Member

    Joined:
    Apr 25, 2021
    Location:
    SF
    Ha, great minds!

    641C00D4-3F2C-46E2-8670-517004C204BE.jpeg
     
  19. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    Normally you would have used a wye and a 45 for that trap.
    The santee and the vent 90 are not what would have passed an inspection.
     
  20. wwhitney

    wwhitney Well-Known Member

    Joined:
    Mar 17, 2019
    Location:
    Berkeley, CA
    So are you going to leave an access panel in your ceiling?

    Agree with Terry--you need to replace the san-tee and white 90 with a wye and a 45.

    Cheers, Wayne
     
  21. Mr tee

    Mr tee In the Trades

    Joined:
    May 3, 2020
    Location:
    Montana
    It looks to me like if the san tee was replaced with a wye that the trap could be piped directly into it without a 45 or 90.

    Will a snake go through that trap?

    I wouldn't want those sj connections in my ceiling.
     
Similar Threads: Looking obscure
Forum Title Date
Plumbing Forum, Professional & DIY Advice Looking for an adapter for faucet to hose (UN to NPT; potable water application) - doesn't exist? Jun 6, 2021
Plumbing Forum, Professional & DIY Advice Looking for mixing valve for HWT May 18, 2021
Plumbing Forum, Professional & DIY Advice Looking for feedback on a water system redesign May 13, 2021
Plumbing Forum, Professional & DIY Advice Looking for a hot stem, 8" wide spread faucet May 5, 2021
Plumbing Forum, Professional & DIY Advice Looking for a fitting in Canada Apr 27, 2021

Share This Page