OK heres my issue, I hope someone can help me out here.

I have a 50 gallon natural gas water tank. Its only about 1 year old.

I do NOT have a Thermal Expansion Tank.

The water is incoming at 44 PSI (one way, no backlflow).

My water tank pressure release valve is set to 120 PSI. A new one was installed just a few days ago.

The water temperature setting on the tank is at level 2 of 5 (low).

The pressure release valve on the water tank is leaking and each morning (not always) there is approx. 100-200 ml of water in a small container underneath the pressure release tube. (1/4 to 1/2 a small bottle of waters worth).

The other day i managed to spot the leaking from the tube. I immediatly put a water pressure gauge on both hot and cold water taps. It registered about 130 PSI.

130 PSI seems very high to me and explains the leaking from the valve.

Is this "normal" for modern day water heaters ?

Do you suspect a problem with the water heater ? Maybe a thermostat problem ?

Should i simply purchase an Expansion Tank ?

If i purchase an expansion tank does the maximum PSI rating need to be above 130 PSI ? or is 100 PSI sufficient ? What about 60 PSI ? (I'm not sure how they actually work for max. PSI purposes).

Should i get 2 Gallon or 4 Gallon ?

Any help would be appreciated. Thank you.
 
Last edited:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
This is a classic example of why you always need an expansion tank when you have a closed system (either with a check-valve or a PRV which acts like one, at least until the internal pressure exceeds the external, IF it has an internal bypass). Add one, and the problem will go away. The tanks can last anywhere from 5-years, to 10 or more, depending on the local water and the luck of the draw. You'll know when it dies...the T&P will start leaking again. Water is not compressible, and when it expands, it has to go somewhere. Often, that may be a leaky valve, expansion of hoses, or if all of those are in good shape, the safety valve (T&P).
 

LeakyLarry

New Member
Messages
4
Reaction score
0
Points
0
Location
Blenheim, ON
Thank you I appreciate your time. Do you have any answers regarding the PSI rating I need for an expansion tank ? Do I need a tank that has a max. PSI rating greater than 130 PSI ? Thank you.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,481
Points
113
Location
Bothell, Washington
Website
terrylove.com
I would get the 2.0 or 2.2 gallon expansion tank for a 50 gallon water heater.
You may have a check valve on the water system, allowing the water heater to pressurize the home beyond what the street pressure is.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
The whole beauty of the expansion tank is that it prevents excessive pressure increases caused by heating the water in the first place. No home should have water pressure greater than 80#, and if you do, you need a PRV. You indicated your static pressure was lower than that, so unless it spikes on its own from the supply (not caused by expansion but from the utility), you don't need a PRV. Just adding the expansion tank, presetting the air pressure before hooking it up to the incoming static pressure value should keep it at that pressure if caused by expansion. Instead of expanding and increasing the pressure in the (barely) inelastic piping, it expands into the bladder of the expansion tank by compressing the air. Since air is quite compressible, the pressure rise is almost not measurable (since a typical WH only expands maybe a max of a pint, and usually less, depending on how much cold was introduced). The tanks generally come pre-charged to 40#...just use a bicycle pump or similar to raise it to your static incoming water pressure before installation. After you install it, and turn on the water, you'll be measuring the water pressure, not the air pressure, so you have to precharge it first.

Any tank, properly sized for a potable water system, should work.

Now, if the pressure DOES spike from the supply, then, you also need to add a PRV.
 

LeakyLarry

New Member
Messages
4
Reaction score
0
Points
0
Location
Blenheim, ON
Thanks alot for the info everyone. I'm sure my noobness has shown through, thats why i need to ask all these questions.

There is already a water reduction regulator doohicky near the main so there is no spike from the outside. All things being "normal" its a static 44 PSI incoming. I have tested the PSI when it is "dormant" at 44 and when it is spiking at 130.

My main concern is the size and PSI rating i need for the expansion tank. As mentioned earlier it spikes to 130 PSI. Does this effect the size and type of tank i get ? (i.e one rated for 60 PSI or one rated for 100 PSI or even 150). Or is this rating thats on the box only a reflection of the incoming PSI ? (i.e 44 PSI i have now). I really need to know this before i go out and purchase one.

Thanks again :).
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
The tank does not need to support that high pressure, since it should never get there except if there is a failure...once installed, the pressure will stay stabilized at your PRV setting and will NOT rise as long as the PRV works and the tank is intact. This should help you size what you need http://www.watts.com/pages/support/sizing_DET.asp
 

LeakyLarry

New Member
Messages
4
Reaction score
0
Points
0
Location
Blenheim, ON
Thank you all again for helping. I've emailed Watts Canada to find out how to purchase a 2 gallon PLT-5 for my area (north of Toronto).
 

Ballvalve

General Engineering Contractor
Messages
3,582
Reaction score
45
Points
48
Location
northfork, california
The guys around here like the bag in a can method of pressure relief, but Watts offers brass valves that should out last a few of them for less money and a very quick install in just about any easy place. Your only price is a few ounces of water a day that can be run into a old campells soup can.

http://www.watts.com/pages/_products_details.asp?pid=803

The problem with the ex tank is that you have no visual indicator of when they fail, they need maintenance which they DO NOT get, and its certain they will. if in doubt, use BOTH.



At 60 pounds pressure, water boils at 307.4 degrees
At 0 pounds pressure, water boils at 212 degrees
At 50 pounds pressure, it releases the same energy as two pounds of dynamite.
 
Last edited by a moderator:

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
I've lived here about 30-years, and have had to replace the grand total of ONE tank...not a very big maintenance issue! If the goal is to maintain an even, safe water pressure and you have a closed system, the only way to keep it from rising with heating the water is an expansion tank. Most pressure relief valves are designed for fault conditions...the are not designed to get used every day. An expansion tank is...
 

Furd

Engineer
Messages
448
Reaction score
2
Points
16
Location
Wet side of Washington State
I have to agree with Jad on this one. The bladder tank will work for years whereas the relief valve, if spitting every day (which would not be uncommon) will fail in a matter of months. Install a servicing valve (ball valve) between the expansion tank and the water supply for ease of maintenance. My preferred method would include a shelf or bracket for the expansion tank and a braided SS hose between the tank and the service valve.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
While I like the idea of a valve between the tank and the line, doing that won't pass code...it sure does make servicing easier, though. The reasoning, as I understand it, is someone could close the valve, and disconnect the tank. If you did, you might take the handle off so it wouldn't happen inadvertently by someone who doesn't know better.
 

Ballvalve

General Engineering Contractor
Messages
3,582
Reaction score
45
Points
48
Location
northfork, california
Maybe you guys should e-mail Watts and have them explain to you that these thermal expansion valves are designed just for everyday expansion and leakage, and in fact that is exactly why they last a very long time.

Sorry, the rubber bag in the campells soup can reeks of failure to me. Springs rule!
 

Furd

Engineer
Messages
448
Reaction score
2
Points
16
Location
Wet side of Washington State
I suspect that the shut-off valves with the spring-loaded reliefs cost less than the rubber bag in the soup can and in the real world initial cost is often the deciding factor rather than lifetime costs. The relief valve WILL spit every time the pressure rises to its set point and that action will erode the seat and disc until it starts dripping continuously. It also wastes water which in some areas is fairly expensive. I have read MANY tales of homeowners that have these reliefs installed and wonder why they have high water bills or why there is a valve in their home that is constantly dripping water to waste.

Jadnashua makes the point that a service valve before the expansion tank won't pass muster with the code inspector and while I disagree with the codes in this instance it also shows that the codes recognize that replacement of an expansion tank is a fairly infrequent event.
 

hj

Master Plumber
Messages
33,613
Reaction score
1,054
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Now, what is the DIFFERENCE between a pressure relief valve that opens to drain off the pressure, and the Watts "pressure limiting valve" which does EXACTLY the same thing? Water heater T&P valves are typically FACTORY set at 150psi, although there are rare ones at 125psi, and they are NOT adjustable, so I am not sure what kind of relief valve you have if it can be "set at 120 psi".
 

Ballvalve

General Engineering Contractor
Messages
3,582
Reaction score
45
Points
48
Location
northfork, california
If one house in 100 in california has a thermal expansion tank, I would be very surprised.

I save them for closed boilers and radiant heat systems.

And in the country, the house without a pressure reducing valve has all the outdoor plumbing and the well expansion tank to absorb those small expansion issues.

The most reliable expansion tank is a hose dripping a bit over the dogs water bowl.
 
Last edited:

LLigetfa

DIYer, not in the trades
Messages
7,632
Reaction score
633
Points
113
Location
NW Ontario, Canada
And in the country, the house without a pressure reducing valve has all the outdoor plumbing and the well expansion tank to absorb those small expansion issues.

The most reliable expansion tank is a hose dripping a bit over the dogs water bowl.

I would think even a city supplied home would have enough frequent consumption to drain off any expansion. My RO system would drain off any excess pressure if I didn't have an air charged tank.

Also would expect hammer stops to act as mini expansion tanks if they are not waterlogged. I installed 6 of the largest hammer stops I could find, each about 16" long and 1" dia. I think they reduce my pump cycling time. :p
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,193
Points
113
Location
New England
Anything that can expand will help. The worst case is starting with a full WH, draining it by say a really long shower, being in the middle of the winter with incoming cold water temps at near freezing, having the WH thermostat set to say 140 or higher, then not using any water while it heats. That would require the maximum volume for your system. Now, not sure how many people do that (if you have teenagers, it may happen often!). Plus, if you are on a well, while technically still required some places, an expansion tank is probably useless, since that tank will absorb the water volume easily. A typical hammer arrester have a very small volume, but as I said, anything that can expand will help. Your washing machine hoses help a bit, too, but they only take so many cycles before they burst. At least with a failed expansion tank, until it has been failed for probably more than a year, won't leak all over and cause major damage. Hopefully, you'd have figured out what was wrong by then and replaced it!

But, adding one is easy, they're cheap, and they work. I don't see much difference between a bladder tank used for your pump and one for thermal expansion...they are essentially the same thing. The expansion tank probably isn't designed to accept the same variation in volume, but it's still a bladder. If you are worried about it, and have a well, change both at the same time the well one dies...the water's off, and you've drained the system, so it only takes a few minutes.

Note, using water during the day has little effect, since the water, after being heated, doesn't change volume (much) if the WH has a decent thermostat.
 
Last edited:

Redwoodvotesoften1

New Member
Messages
76
Reaction score
0
Points
0
The most reliable expansion tank is a hose dripping a bit over the dogs water bowl.

Dang Dat'll be the way ma still duz it. Werks rite by me. I dunno if id put ma prayerz inta havin wun o dem expandin tanks keepin ma still frum gittin blowed up.

Say Ballvalve dem pitchers ya'll put up of yer north 40.

attachment.php


Imma thinkin we mite git tagether n set up a cupulla stills der.
Dat be sum dang fine place ta do it in ma mind.
we kin prolly grewed a croppa wildwood weed to.

A lil bitta tax free incum never hurt nobuddy.
 
Last edited by a moderator:

Ballvalve

General Engineering Contractor
Messages
3,582
Reaction score
45
Points
48
Location
northfork, california
At pot harvest time, you can watch the helicopters study the canyons. Used to be quite the dangerous place to hike.

Not too sucessful anymore, fire cleaned it up, not enough tree cover or roads, and as you can see, a guy with binoculars can watch the whole world.

Trouble with stills is that after all the work, the $8.99 vodka is better and cheaper at the store.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks