I have back to back bathrooms and need to figure out how I can plumb toilets to code in KY. I want to keep the main line up in the joist space so I can finish the ceiling in the basement. The inspector said I can use a double cross tee but if when I add a 90 at the bottom and need to 1/4' fall 20' away this will put line below bottom of joist. I was wondering if I could connect to main line horizontally. Can vents be in main line?

Thanks,
Tom
 

Attachments

  • Toilet layout.pdf
    17.4 KB · Views: 270

James Henry

In the Trades
Messages
1,580
Reaction score
404
Points
83
Location
Billings, Montana.
here's something to try.
 

Attachments

  • Untitled.png
    Untitled.png
    84.8 KB · Views: 368

wwhitney

In the Trades
Messages
6,583
Reaction score
1,853
Points
113
Location
Berkeley, CA
The OP is talking about a double sanitary tee (maybe should be a double fixture fitting?) with the inlet and outlet vertical, and then putting a ninety on the bottom to turn horizontal, then going 20' horizontally, and the required fall for that 20' run would put him below the bottom of the joists at the end of that run.

If using a double sanitary tee (or double fixture fitting), would it be allowed to tilt it 45 degrees, so that it would only take another 45 at the outlet to turn horizontal? That would save quite a bit of height.

Cheers, Wayne
 

wwhitney

In the Trades
Messages
6,583
Reaction score
1,853
Points
113
Location
Berkeley, CA
Also, would a flat wye with 2" side inlet be a code compliant way to combine the two horizontal toilet drains, and vent them jointly via the vertical 2" side inlet? This would keep the toilet drains horizontal, unlike using a (double) sanitary tee, which requires a vertical section of drain.

Cheers, Wayne
 

James Henry

In the Trades
Messages
1,580
Reaction score
404
Points
83
Location
Billings, Montana.
The OP is talking about a double sanitary tee (maybe should be a double fixture fitting?) with the inlet and outlet vertical, and then putting a ninety on the bottom to turn horizontal, then going 20' horizontally, and the required fall for that 20' run would put him below the bottom of the joists at the end of that run.

If that is what he is talking about, then, he should look up his in local code, in the drainage section, table 704. "slope of drainage pipe".
In the IPC, 3" or larger is allowed to slope 1/8" per foot, that should make it work for him.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
This is a rough draining. There should be wyes and long turn 90's here, but the concept is there.
Two toilets on the horizontal with one vent works using a wye like the way James showed.