I am adding a new bathroom on the main floor and the current drainage exits the basement through a high line. I've been told "there isn't enough room in this stack" and it needs to be totally redone. My first question is, based on the picture could I run the tub drain into a side inlet tee with the toilet sani-tee? Or perhaps combine the tub and ejector with a wye (above or below the toilet)? This would free up the room I need, basically I need to bring in another 4" drain pipe. I will be adding a toilet, lav, shower and washer which will all be vented with AAM's. Thanks

side view stack1.png
front view stack1.png
 
Last edited:

Breplum

Licensed plumbing contractor
Messages
1,966
Reaction score
798
Points
113
Location
San Francisco Bay Area
I'd rebuild using 3" no-hub for the entire stack. Up to three WCs and all the rest are allowed on 3" (or stick with 4"). Certainly your new additions can also be on a 3" line as well.
I would make the existing WC a 3" line and bring it up higher. Then, right below that, a double 3 x 2 wye, with the right side picking up the ejector, the left side can then pick up the tub.
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
The santee and wye 2 uppermost fittings would need to come out at a minimum its possible that part could be saved .
3 inch is fine for your addition
 

DaveTaylor

New Member
Messages
3
Reaction score
0
Points
1
Location
Michigan
Thanks for the input but I'm still confused. 99% sure I'm going to have a plumber tackle this but I still want to know what's going on.

Basically, I think everything dumps into this vertical which is a wet vent for the toilet. The bathroom sink is at the top I assume, draining into it and using it as a vent. The first fitting from the top (tee) is a vent for the ejector pit. Then there is a wye fitting for the bathtub. I thought the tub is using the vent stack for venting as well, but I could be mistaken. Then we have the 4" from the toilet and finally the tee for the ejector pit discharge.
Would anyone be willing to draw a mockup of how I could get all of this connected, along with an additional 3 or 4 inch waste line coming in from the right?
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
How is the tub vented?

The only thing draining into the top of the stack shown is a lav?

I'm pretty sure that the ejector pit vent should rise to the story above and connect to the lav's vent at least 6" above the lav flood rim, rather than connecting to the lav drain.

Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
I can't draw it but, to save the stack, the top tee needs to go higher and the wye below that is removed to allow a wye to serve the addition the tub line will relocate by connecting somewhere in toilet branch.
 

Jeff H Young

In the Trades
Messages
8,954
Reaction score
2,235
Points
113
Location
92346
Top santee was a vent for pump? No way should vent be tied below flood level of lav . If your plumber is competent and good I see no reason to object to building stack or whether you are going to get a better or cheaper job done by saving it
 
Last edited:

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,459
Points
113
PS. The ejector piping should be run in pressure rated pipe and fittings and its discharge is rated the same as 4" gravity drain is the reason why you can't combine it with another fixture. It also should be the Most downstream connection to the stack as it is in this scenario. Combining it with another fixture as a double wye on the vertical is also acceptable.
 