When I upgrade low efficiency furnace, do I need to upgrade the hot water tank?
Beets
Manitoba
I have a 19 year old low efficiency gas furnace and water tank. I want to add air conditioning. I suspect the best path forward is to replace the furnace with one that has AC rather than retrofitting an old furnace with AC. I suspect that any new furnace I purchase will be mid or high efficiency and have a PVC exhaust. Can that exhaust under a veranda? If not, I don't have any great place to exhaust without a very long horizontal run. Any idea as to the max Hz run? Can the exhaust go up through the roof using the existing chimney or does it need to be PVC to get high enough velocity? The chimney is shared with my hot water tank. Would they need to sleeve the chimney with PVC? Is that easy? Would hot water tank need to be changed at the same time to mid or high efficiency? Most of my basement is fully finished, so routing the exhaust is a concern.
Fitter30
Peace valley missouri
Brand of furnace flue max length has some variables size of pipe and number of elbows (90*s) . Flue can be run under veranda but not outlet exhaust. PVC flue can't be mix galvanized 90%+ furnace flue gas is very corrosive. New furnace with matching coil in cabinet is best for proper air flow through the furnace and coil.
https://www.seerenergysavings.com/ Check with your utility companies for rebates. Since you don't have central air a manual j heat load should be run to see what tonnage unit needed.
Dana
In the trades
At a minimum the water heater venting with a narrowing liner would need to be changed to avoid destructive condensation inside the chimney, but you may run into code problems sharing the chimney as a flue chase for PVC venting + combustion AND a metal low-efficiency combustion appliance liner.
It might be better to just swap out the water heater for a heat pump (electric) water heater, which needs no flue, and would allow you to seal up the chimney for less 24/365 stack effect induced infiltration.
BTW: Rather than just replacing an oversized low efficiency furnace for a high efficiency version with the same capacity is almost always a mistake. The vast majority of furnaces are sub-optimally oversized for their loads, and operate at too low a duty cycle to provide real comfort. You don't really need to cover the theoretical heat load when it's -100C outside, after all. The 99% outside design temps in most of Manitoba are ~ -25C or warmer, and if -24C was your design temp a furnace with no more capacity than the load at -40C would cover even the most severe cold snaps. Going with more capacity than 1.4x the load at the local 99% outside design temp results in LESS comfort rather than more. At 1.4x oversizing the furnace is running (1/1.4=) 71% of the time at design condition. At the commonly found 3x oversizing it's only running 33" of the time at design condition, and off the other 67% of the time. From a comfort point of view it's akin the difference between taking a 5 minute 2gpm shower vs dumping 10 gallons of hot water on your head.
To figure out what your actual design load is, use the old furnace as the measuring instrument by logging fuel use against wintertime heating degree-day data, as outlined here.