Hi All, first time posting here but I've learned so much just browsing as a non-member. Thanks to Terry Love for hosting this site! Hope I won't be banned for life after this extended post! . Can anyone firm-up my knowledge of wet venting, specifically in King Co. WA (Seattle)? I think I've learned the following:
• General idea: a pipe that drains another fixture can, under the right circumstances, have enough air flowing above any draining water to simultaneously serve as a vent for a fixture downstream.
• General Requirements:
My specific questions are:
1. Is the 2" pipe shown sufficient to wet vent the floor drain? I think it is since I've read that a 2" pipe can wet vent 4 fixture units and the laundry box is just 2 units.
2. If I want to claim that the same pipe is wet venting the toilet as well, do I need to go up to 3" (since the toilet will add another 3 fixture units, bring the total to 5 units)? If so, when can that 3" be reduced to 2"? At the intersection with the laundry box dry vent I'm assuming.
3. The toilet is just about exactly 6' from the main 4" stack if I measure along the pipe path, closer as the crow flies. Should I just call it good for that vent? I guess that's probably inspector dependent, and yes, this is all permitted work will be inspected.
Thanks in advance for any help/advice!
Jonathan
• General idea: a pipe that drains another fixture can, under the right circumstances, have enough air flowing above any draining water to simultaneously serve as a vent for a fixture downstream.
• General Requirements:
* the section of pipe serving as a wet vent cannot be draining a toilet.
* the pipe serving as a wet vent must be sized correctly (i.e. large enough for the general idea above to actually work).
* the length of the wet vent section is not limited by code
Of course I have a specific situation in mind, and related questions. In the attached diagram I would like to wet vent the floor drain, and maybe the toilet. All the pipe in the studio will be under a 4" concrete slab or embedded in the footing at the edge of this monolithic concrete pour, i.e. the 2" pipes for the laundry box and the sink run though the footing. * the pipe serving as a wet vent must be sized correctly (i.e. large enough for the general idea above to actually work).
* the length of the wet vent section is not limited by code
My specific questions are:
1. Is the 2" pipe shown sufficient to wet vent the floor drain? I think it is since I've read that a 2" pipe can wet vent 4 fixture units and the laundry box is just 2 units.
2. If I want to claim that the same pipe is wet venting the toilet as well, do I need to go up to 3" (since the toilet will add another 3 fixture units, bring the total to 5 units)? If so, when can that 3" be reduced to 2"? At the intersection with the laundry box dry vent I'm assuming.
3. The toilet is just about exactly 6' from the main 4" stack if I measure along the pipe path, closer as the crow flies. Should I just call it good for that vent? I guess that's probably inspector dependent, and yes, this is all permitted work will be inspected.
Thanks in advance for any help/advice!