hj
Master Plumber
- Messages
- 33,608
- Reaction score
- 1,047
- Points
- 113
- Location
- Cave Creek, Arizona
- Website
- www.terrylove.com
pipe
1. IF you were to connect to that pipe in the corner for the drain, you could NOT use a Y and 1/8 bend, unless you also installed a proper vent.
2. You CANNOT tie a vent into that corner pipe, IF it is a drain from an upper floor fixture.
3. You can connect to that pipe at a point 6" above the overflow level of that fixture, or 42" above that floor level, whichever is HIGHER.
1. IF you were to connect to that pipe in the corner for the drain, you could NOT use a Y and 1/8 bend, unless you also installed a proper vent.
2. You CANNOT tie a vent into that corner pipe, IF it is a drain from an upper floor fixture.
3. You can connect to that pipe at a point 6" above the overflow level of that fixture, or 42" above that floor level, whichever is HIGHER.