Working through the math for system flow, tube sizing, and head loss has me a bit stumped. I get the math and know that the formula for heat transfer is an, but here's an example that illustrates my issues:
Say I have a level in the house that has a 15,000 BTUh design load (99% design temp of -8 F in St. Paul, MN which shouldn't really matter for this discussion). Figure on 5 identical emitters, each rated to put out 3,000 BTUh at 140F supply temp to heat the space. Assume Delta T of 30F. f = Q/500 x (∆T) gives a target flow rate of 15,000/500*30 = 1 gpm for the entire level, or 0.20 gpm per emitter.
Now its's time to pick tube size. Best practice suggests flow velocities between 2 fps - 4 fps.
v = 0.4084 f(gpm)/d (in) ^2. For a tube diameter of 0.5", this yields 0.4084 * 0.20 * 0.25 = 0.33 fps. Way too low. Tube diameter of 3/16" gets us to a flow velocity of 2.32 fps - right around the recommended low velocity limit to insure removing air bubbles, etc. That's a really small tube diameter., and the head loss would be ridiculous.
Now to head loss. Say I'm planning to set each emitter up as a home run off a manifold. My longest circuit is equivalent to 100 ft of 0.5" tubing. HL = k x c x L x f^1.75. Assume k of 0.04 for 1/" PEX-Al-PEX; c of 1.00 (close enough , for water at average temp of 125F); L = 100 ft; 0.20^1.75 = 0.06. HL = 0.28 ft. Very low, but my flow velocity is way too low. I can't find any values of k for 3/16" PEX, but say it existed and extrapolate from published values for available sizes. You'd have a k somewhere around 4, and doing the math gives a head loss of around 29 ft. Ridiculously high in order to achieve a flow velocity of 2.32 fpm.
I get that flow restrictors could tune the flow rate to a target flow of ~0.2 gpm at each emitter, but the flow velocity everywhere except through the restrictor will be too low.
What am I missing or where are my errors?
Say I have a level in the house that has a 15,000 BTUh design load (99% design temp of -8 F in St. Paul, MN which shouldn't really matter for this discussion). Figure on 5 identical emitters, each rated to put out 3,000 BTUh at 140F supply temp to heat the space. Assume Delta T of 30F. f = Q/500 x (∆T) gives a target flow rate of 15,000/500*30 = 1 gpm for the entire level, or 0.20 gpm per emitter.
Now its's time to pick tube size. Best practice suggests flow velocities between 2 fps - 4 fps.
v = 0.4084 f(gpm)/d (in) ^2. For a tube diameter of 0.5", this yields 0.4084 * 0.20 * 0.25 = 0.33 fps. Way too low. Tube diameter of 3/16" gets us to a flow velocity of 2.32 fps - right around the recommended low velocity limit to insure removing air bubbles, etc. That's a really small tube diameter., and the head loss would be ridiculous.
Now to head loss. Say I'm planning to set each emitter up as a home run off a manifold. My longest circuit is equivalent to 100 ft of 0.5" tubing. HL = k x c x L x f^1.75. Assume k of 0.04 for 1/" PEX-Al-PEX; c of 1.00 (close enough , for water at average temp of 125F); L = 100 ft; 0.20^1.75 = 0.06. HL = 0.28 ft. Very low, but my flow velocity is way too low. I can't find any values of k for 3/16" PEX, but say it existed and extrapolate from published values for available sizes. You'd have a k somewhere around 4, and doing the math gives a head loss of around 29 ft. Ridiculously high in order to achieve a flow velocity of 2.32 fpm.
I get that flow restrictors could tune the flow rate to a target flow of ~0.2 gpm at each emitter, but the flow velocity everywhere except through the restrictor will be too low.
What am I missing or where are my errors?