I live in a 2-story single family house in Wisconsin that has a full basement below grade. I am adding a new full bath in the basement and there was no rough-in done earlier. There are two 3” drain stacks that come down into the basement from the upper floors. Notice in the picture below, the locations highlighted for the two 3” drain stacks (#1 and #2), vent stack (#3), new wet bar sink (#4) and the cleanout plug (#5) in the floor from where the building drain must be exiting the house to connect to the city sewer outside –
The location of the new bathroom in the basement is right under the ½ bath on the first floor. Notice that there is a 3” drain stack (#2) right next to the location of the new bathroom. Before digging the concrete floor, I was thinking of connecting the new bathroom fixture drains to that drain stack. After digging and seeing how the drain pipes are laid out, it is clear that the #2 3” drain stack turns quickly away from the new bathroom location and heads toward the building drain not leaving much height to connect the new bathroom fixtures. However, the 3” drain stack coming from the back wall (#1) is passing right under the new bathroom location. The vent stack (#3 with blue highlight) goes under the concrete floor, turns horizontal and connects to the 3” drain pipe (#1) coming from the back wall.
Now I am thinking that I might be able to connect the new bathroom fixtures as well as the wet bar sink to #1 3” drain pipe instead of #2 drain stack. The question is what is the best way to vent these fixtures. Given that the vent pipe (#3) is connecting to the drain pipe #1 right under the floor of the new bathroom location, can all the new bathroom fixtures and the wet bar sink be “wet vented” by the #1 drain pipe? Or do they need to be vented separately because the dry vent pipe #3 has already gone horizontal under the new bathroom fixtures’ flood level rim?
Here is the view from the side (behind the bathroom sink) showing relative location of the new bathroom fixtures, the wet bar sink (across the stairs), the vent pipe #3 and drain pipe # 1–
Here is some information about the existing drainage load on the two 3” drain stacks –
Total new DFU’s to be added by the full bath and the wet bar sink = 9
Here are the distances from the new basement fixtures to the existing drain pipe #1 –
Here is a close-up of how the dry vent #3 connects to drain pipe #1 –
The location of the new bathroom in the basement is right under the ½ bath on the first floor. Notice that there is a 3” drain stack (#2) right next to the location of the new bathroom. Before digging the concrete floor, I was thinking of connecting the new bathroom fixture drains to that drain stack. After digging and seeing how the drain pipes are laid out, it is clear that the #2 3” drain stack turns quickly away from the new bathroom location and heads toward the building drain not leaving much height to connect the new bathroom fixtures. However, the 3” drain stack coming from the back wall (#1) is passing right under the new bathroom location. The vent stack (#3 with blue highlight) goes under the concrete floor, turns horizontal and connects to the 3” drain pipe (#1) coming from the back wall.
Now I am thinking that I might be able to connect the new bathroom fixtures as well as the wet bar sink to #1 3” drain pipe instead of #2 drain stack. The question is what is the best way to vent these fixtures. Given that the vent pipe (#3) is connecting to the drain pipe #1 right under the floor of the new bathroom location, can all the new bathroom fixtures and the wet bar sink be “wet vented” by the #1 drain pipe? Or do they need to be vented separately because the dry vent pipe #3 has already gone horizontal under the new bathroom fixtures’ flood level rim?
Here is the view from the side (behind the bathroom sink) showing relative location of the new bathroom fixtures, the wet bar sink (across the stairs), the vent pipe #3 and drain pipe # 1–
Here is some information about the existing drainage load on the two 3” drain stacks –
3” Drain stack #1 | 1st floor kitchen, 2nd floor full bath | 11 DFU’s |
3” Drain stack #2 | 1st floor ½ bath, 1st floor washing machine, 2nd floor full bath | 17 DFU’s |
Total new DFU’s to be added by the full bath and the wet bar sink = 9
Here are the distances from the new basement fixtures to the existing drain pipe #1 –
Bathroom Shower | 30” |
Bathroom Toilet | 45” |
Bathroom Sink | 6’ |
Wet Bar Sink | 9’ |
Here is a close-up of how the dry vent #3 connects to drain pipe #1 –