Residential power problem. Burning up surge protectors on a 15 branch circuit with no load on it. Over 2 weeks, various light flickering, dimming, etc. Finally 3rd surge protector burned up, found cb tripped on the branch feeding the sp that burned up, 15 amp arc fault. One 120VAC leg to main disconnect had 240VAC on it, the other had 4VAC. Called power company, when they showed up, legs were normal at 120VAC. Can't help but think transformer has to be possessed. 2nd time they came out to check meter base, even put load on it, checked ok. Loosing my mind. When reading 240VAC on one leg, lights in house that did work obviously were exceptionally bright. Transient situation again over 2 weels. Any ideas? Thank you. UPDATE
After burning out 2 bed motors, 2 ovens, range top, 2 refrigerators, ceiling fan, 2 garage door openers, etc, they finally looked at the transformer, the neutral lug on the can had never been tightened down, 5 years after installation. They said they would pay all damages. This took 2 weeks and 3 trips by linemen to find.
After burning out 2 bed motors, 2 ovens, range top, 2 refrigerators, ceiling fan, 2 garage door openers, etc, they finally looked at the transformer, the neutral lug on the can had never been tightened down, 5 years after installation. They said they would pay all damages. This took 2 weeks and 3 trips by linemen to find.