Hello all,
I am just about to put my drywall up and want to make sure my PEX water supply lines are good to go. I have a hot and a cold 3/4" main line going to a manifold reducing down to 1/2". I looped at the shower lines (shower valve not installed) and capped the rest. I put the pressure at 80PSI and loose about 5-6PSI over 3 hours. I did re-crimp all the fittings and went around with soap water ( no bubbles to be seen). Now I wonder if the 5-6PSI drop over 3 hours is acceptable and due to expanding lines, air temperature from compressed air, change in outside temperature? Any ideas and input would be really appreciated since I want to be confident in the system before I cover everything with drywall.
Thank you so much
I am just about to put my drywall up and want to make sure my PEX water supply lines are good to go. I have a hot and a cold 3/4" main line going to a manifold reducing down to 1/2". I looped at the shower lines (shower valve not installed) and capped the rest. I put the pressure at 80PSI and loose about 5-6PSI over 3 hours. I did re-crimp all the fittings and went around with soap water ( no bubbles to be seen). Now I wonder if the 5-6PSI drop over 3 hours is acceptable and due to expanding lines, air temperature from compressed air, change in outside temperature? Any ideas and input would be really appreciated since I want to be confident in the system before I cover everything with drywall.