Hello All.

Had to get a new hot water heater today as my old one started leaking after 9 years. I replaced it with the exact same model (40 gallon Rheem low boy, natural gas, normal venting) and finished installing it a couple of hours ago.

When I disconnected the vent from the old one, I noticed a lot of debris in the horizontal duct leading to my chimney. I do not have a chimney liner so it vents direct into the 1920's masonry chimney. I cleaned it out the best I could and will call a chimney guy tomorrow and most likely get a liner installed and finally change the configuration of the vent pipes (my natural gas boiler vent enters the chimney above the hot water heater vent and I was told that is a no-no as but never got around to getting it modified).

My question is that the vent pipe for the new hot water heater is extremely hot, like very hot...like it sizzles when I touch a wet rag to it. It read 280 degrees in one section on my infrared temperature gun. It is a single wall vent pipe, and I do not make a habit of touching them regularly to get a good comparison, but still seems way hotter than it should be.

My CO2 detector is about 6 feet away and has not gone off yet so that is good news. My question is should the vent pipe get that hot? Maybe because it is heating a full tank of cold water?

IMG_1020.jpg
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
Installing a gas/combustion fixture DIY is ill advised, both fire and CO hazard - in this case, the riser off the heater is too short, not knowing that tank's height, you might have purchased a shorter heater to resolve it.
 

Weekend Handyman

Active Member
Messages
437
Reaction score
131
Points
43
Location
Nova Scotia
Installing a gas/combustion fixture DIY is ill advised, both fire and CO hazard - in this case, the riser off the heater is too short, not knowing that tank's height, you might have purchased a shorter heater to resolve it.
It always amazes me when folks choose to do their own gas work. I will DIY most plumbing projects, limit myself to basic electrical work, but won’t touch gas or oil with a 10 ft pole. The consequences are just too high … a flood is one thing, an explosion is quite another.
 

Weekend Handyman

Active Member
Messages
437
Reaction score
131
Points
43
Location
Nova Scotia
280° is in range. If there's a drafting problem the first sign is melted plastic around the water piping next to the draft hood.
Is that shark bite supply line close enough to the flue pipe to get fried? Looks like it is pretty much touching.
 

Tuttles Revenge

In the Trades
Messages
4,205
Reaction score
1,459
Points
113
It always amazes me when folks choose to do their own gas work. I will DIY most plumbing projects, limit myself to basic electrical work, but won’t touch gas or oil with a 10 ft pole. The consequences are just too high … a flood is one thing, an explosion is quite another.
While I'm happy that people are afraid of gas.. I just don't understand why.
Is that shark bite supply line close enough to the flue pipe to get fried? Looks like it is pretty much touching.
Yeah.. that looks WAY too close.
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
While I'm happy that people are afraid of gas.. I just don't understand why.

Yeah.. that looks WAY too close.
Every winter here after heat kicks on, there's are news stories once/twice a month about CO poisonings, fire or explosions due to faulty installs.

The CO one's are particularly sad & scary, families die in their sleep.
 

Oldspicesocal

New Member
Messages
18
Reaction score
0
Points
1
Location
California
Every winter here after heat kicks on, there's are news stories once/twice a month about CO poisonings, fire or explosions due to faulty installs.

The CO one's are particularly sad & scary, families die in their sleep.
It looks fine don’t listen to this guy, as long as it slopes up and recommended 12” riser before an elbow
Installing a gas/combustion fixture DIY is ill advised, both fire and CO hazard - in this case, the riser off the heater is too short, not knowing that tank's height, you might have purchased a shorter heater to resolve it.
 

Fitter30

Well-Known Member
Messages
4,372
Reaction score
800
Points
113
Location
Peace valley missouri
Top joint off water heater looks like the crimped end isn't shoved in far enough metal tape doesn't cut it each joint should have three screws per joint. Install manual probably wants 12" straight pipe off the top before a ell. Furnace and water flue wh should be on top of the furnace flue. Just because it's always been on the bottom most codes wh on top.
 

Nebojsa

Member
Messages
72
Reaction score
11
Points
8
Location
Ontario
I had a similar setup. Replaced it after having a chimney liner installed to prevent the bricks from deteriorating further from the condensation especially during winters. I have both flues join into one just before entering the wall.
 

Jeff H Young

In the Trades
Messages
8,957
Reaction score
2,235
Points
113
Location
92346
Installation not greatest . Ive had many that couldnt have a straight shot for a foot off the draft hood, but thats only one of the issues . Its good you plan on improving things , Some are easily achieved some are not I too dont care for the water lines being too close to heat of vent easy to improove on that. glad to hear you have CO detectors good idea for us all to have!
As far as the dangers of working on a gas connection lighting a pilot or hooking up a union I think some of the comments are hysterical phobias. People die from stupid mistakes yes drunk driving , sober driving , hooking up water heaters is down there on the lower end of risks but the consequences can be high. crossing a street walking to school should be illegal for children right?
 

GReynolds929

Active Member
Messages
354
Reaction score
115
Points
43
Location
WA
It looks fine don’t listen to this guy, as long as it slopes up and recommended 12” riser before an elbow
I'd like to see a source for the 12" rise. The manuals for the water heaters we install don't have this requirement.
 

Jeff H Young

In the Trades
Messages
8,957
Reaction score
2,235
Points
113
Location
92346
A O smith ultra low nox 50 gal gas water heaters recomend in the manual but dont require 12 inches verticle rise befor the first 90. It could be because these are ultra low nox and not just low nox ?
 