It's an older gas boiler (late 80's Raypak H3-135B), it's was beginning to make so noise from boiling when it was approached the high limit shut off. I took apart the boiler yesterday and cleaned the outside of the heat exchanger (there was a fair bit of debris in it that has made it's way down the chimney). Cleaning it did help but it was still making noise from 190°F to 195°F (after cleaning). Before started at 180°F- 185°F.
I figured turning the dial would change the high cut off limit. Is the arm on the dial to set the differential? would moving that either way change the differential?
I would have cleaned the inside of the heat exchanger but didn't have new seals for putting it back together. And i can live with some noise and heat, as opposed to no noise and no heat.
It's a 2 stage boiler (yes it's way oversize) and I have already disabled the 2nd stage so it runs about at half (~60 kbtu based on the manual, not sure if that is input or output), but it can keep up on the coldest days. With both stages going it would make a lot more noise. The second stage has been disabled for a few years.
It may also be one of the circulators is getting weak and not flowing as much as it should.