    Current setup:

    Well pump filling 325 gallon vented tank via float switch.
    Countyline CLTS5 drawing from storage tank and flowing through a Fleck 2510 AIO aeration filter then to a 85 gallon pressure tank then to the home.

    Countyline has inlet and outlet check valves. Pressure switch set to 40 cut in and 60 cut off.

    Problem: once countyline reaches 60psi it shuts off but pressure drops to 45psi per pressure gauge mounted on outlet. Pressure slowly drops until it reaches 40psi then pump kicks on. This cycle repeats about every 10 mins or less.

    Problem #2: I also noticed that sometimes, the pump will reach 60psi then the pressure switch will cycle from 60 - 40 psi (so on, off, on, off and so on) very quickly until we unplug the pump.

    We've looked for leaks in both inlet and outlet without any evidence.

    Question: Any idea why the pressure drop once we reach 60psi? Wouldn't it hold there once that pressure is reached?

    FYI - check valves were installed for troubleshooting purposes. The issue is present with and without the check valves.
     
    Last edited: Aug 1, 2020 at 8:58 AM
  2. valveman

    valveman Cary Austin Staff Member

    Joined:
    Mar 15, 2006
    Occupation:
    Pump Controls Technician
    Location:
    Lubbock, Texas
    Close the ball valve on the line going to the house. If the water is not leaking at the house, then the check valve(s) no matter how many, are not holding. You only need one check valve in the suction line from the storage tank to the pump.

    Also the pressure switch being too far from the tank can cause the quick on/off on/off you see, especially if there is a check valve between the pump and pressure tank.
     
    Chris Dickerson likes this.
  3. Sponsor

    Sponsor Paid Advertisement

     
    Chris Dickerson likes this.
  4. Chris Dickerson

    Chris Dickerson New Member

    Joined:
    Saturday
    Location:
    BEDIAS TEXAS
     
  5. valveman

    valveman Cary Austin Staff Member

    Joined:
    Mar 15, 2006
    Occupation:
    Pump Controls Technician
    Location:
    Lubbock, Texas
    All gauges should read 60 just as the pump shuts off. Then if the check valve is holding and no one is using water the pressure should stay at 60 until someone opens a faucet.
     
  6. valveman

    valveman Cary Austin Staff Member

    Joined:
    Mar 15, 2006
    Occupation:
    Pump Controls Technician
    Location:
    Lubbock, Texas
    All gauges should read 60 just as the pump shuts off. Then if the check valve is holding and no one is using water the pressure should stay at 60 until someone opens a faucet.
     
Similar Threads: County line
Forum Title Date
Pumps and Tanks Well Forum & Blog. Water is life. Add jockey pump to county water connection Jul 8, 2019
Pumps and Tanks Well Forum & Blog. Water is life. County water with low pressure at the meter location May 25, 2018
Pumps and Tanks Well Forum & Blog. Water is life. 2" well driller in Brazoria County May 27, 2014
Pumps and Tanks Well Forum & Blog. Water is life. Orange County mud May 1, 2011
Pumps and Tanks Well Forum & Blog. Water is life. Well Or County Water???? Mar 9, 2008

Share This Page