Check the water pressure. Higher pressure will cause the water to flow faster in the pipes. The Copper Institute has defined some maximum water velocity specifications for hot and cold copper pipes. For hot, the maximum velocity is 5fps, which is only 4gpm with a 1/2" line, and 8gpm on a 3/4" line. Water speeds up when it hits a restriction (but that also creates more friction). Static water pressure drops about 0.4#/foot elevation, so the pipes on the third floor will have less pressure, but not all that much (maybe a couple of pounds or a bit more). On cold pipes, they allow the water to flow faster, I think it's 8fps. Excessive velocity can cause water flow noises, and maybe more critical, actual erosion of the pipe from the inside.
If your static water pressure is >80psi, you need a pressure reduction valve and an expansion tank since the PRV will create a closed system, and heated water needs a place to expand that it could (likely) do into the supply prior to the addition of a PRV. Dynamic pressure will vary depending on the length and diameter of the pipes, the velocity, and the number of elbows/tees/etc. in the system.
It could be just that they didn't anchor the pipes well, but that is harder to check...check the pressure first.