we have ordered a new contactor but I'm not sure that's the problem any more! Our ac is always on unless we shut it off at the breaker. The contactor is constantly engaged but if we disconnect a wire it pops out. So it's only stuck on because it always has voltage, the actual contact points aren't welded or pitted or anything....what would cause this? A bad relay switch on the furnace board? A short?
 

Bgard

Member
Messages
113
Reaction score
24
Points
18
Location
NW Indiana
most likely the thermostat itself, remove the thermostat from it's sub base and see if it shuts off the. is it just the out door unit the keeps running or the fan inside also? either way removing the thermostat would be the first place to check.
 

Reach4

Well-Known Member
Messages
38,924
Reaction score
4,447
Points
113
Location
IL
Or probe the wires/terminals to or at the thermostat.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
A model number would help.

I agree T-stat unless it has a exotic controller.
 

Guyerme

New Member
Messages
2
Reaction score
0
Points
1
Location
Illinois
It's a Honeywell lyric T5, we just replaced it last month. I pulled it off the base where the wires attach and the ac stayed on. When it started doing this a few weeks ago first nothing would turn on and the furnace gave me a 24 error so I replaced the fuse on the furnace board and the system kicked back on but then everything stayed on all the time!

I think it's just the outdoor unit. Before we realized what it was doing the pipes kept freezing up because it was constantly running although the air wasn't circulating.
 

Stuff

Well-Known Member
Messages
1,221
Reaction score
130
Points
63
Location
Pennsylvania
This sounds a lot like wires that are shorted/pinched somewhere. Could be behind the thermostat base or even in the furnace.
 

Tony Hwang

New Member
Messages
8
Reaction score
0
Points
1
Location
Calgary, AB
most likely the thermostat itself, remove the thermostat from it's sub base and see if it shuts off the. is it just the out door unit the keeps running or the fan inside also? either way removing the thermostat would be the first place to check.

+1, control voltage is always present which is originating from thermostat Y terminal. Analog or digital thermostat? Trouble-shoot with multi meter.
 

WorthFlorida

Clinical Trail 5th session completed 4/24/24.
Messages
5,769
Solutions
1
Reaction score
1,000
Points
113
Location
Orlando, Florida
If it was the thermostat the fans both inside and outside would be running. The outside contractor also turns on the condenser fan but some units l have a small circuit board if there is a two speed fan.

The control board inside the air handler probably went bad. You did blow a fuse. You need to trace back the wire from the compressor relay back to the air handler. Look for any burn marks on the control board. FYI 24v ac operates the contactor.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
It's a Honeywell lyric T5, we just replaced it last month. I pulled it off the base where the wires attach and the ac stayed on. When it started doing this a few weeks ago first nothing would turn on and the furnace gave me a 24 error so I replaced the fuse on the furnace board and the system kicked back on but then everything stayed on all the time!

I think it's just the outdoor unit. Before we realized what it was doing the pipes kept freezing up because it was constantly running although the air wasn't circulating.

Was the fuse that blew the one for the T-Stat transformer ?

If that voltage is missing the outside unit may run, But the inside blower may not.

Good Luck. Never use a bigger fuse.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
With the thermostat off (i.e., not calling for cooling), double-check the voltage at the contactor's coil. If it has 24vac across it, double check it at the thermostat base. It should be open. without the thermostat in the circuit, if there's 24vac on the yellow to common, there's a short somewhere.

Essentially, the thermostat is just a smart switch...when cooling is called for, it connects the R to Y to supply voltage to the ac contactor (the return line is wired from the ac unit to the source of the 24vac). That turns the ac unit on. It may or may not immediately turn on the circulation fan.

IOW, you're looking for where the coil is getting 24vac when the thermostat is not calling for cooling. It could be a defective thermostat, a connection between the R and Y somewhere else, or a defective contactor, but that doesn't seem to be the case. But, if you miswired the contactor, it's possible it could be getting the coil energized, but it would be a weird set of circumstances.
 