Contactor stuck on always has voltage
Guyerme
Illinois
we have ordered a new contactor but I'm not sure that's the problem any more! Our ac is always on unless we shut it off at the breaker. The contactor is constantly engaged but if we disconnect a wire it pops out. So it's only stuck on because it always has voltage, the actual contact points aren't welded or pitted or anything....what would cause this? A bad relay switch on the furnace board? A short?
Bgard
Active Member
NW Indiana
most likely the thermostat itself, remove the thermostat from it's sub base and see if it shuts off the. is it just the out door unit the keeps running or the fan inside also? either way removing the thermostat would be the first place to check.
Or probe the wires/terminals to or at the thermostat.
DonL
Houston, TX
A model number would help.
I agree T-stat unless it has a exotic controller.
Guyerme
Illinois
It's a Honeywell lyric T5, we just replaced it last month. I pulled it off the base where the wires attach and the ac stayed on. When it started doing this a few weeks ago first nothing would turn on and the furnace gave me a 24 error so I replaced the fuse on the furnace board and the system kicked back on but then everything stayed on all the time!
I think it's just the outdoor unit. Before we realized what it was doing the pipes kept freezing up because it was constantly running although the air wasn't circulating.
Stuff
Pennsylvania
This sounds a lot like wires that are shorted/pinched somewhere. Could be behind the thermostat base or even in the furnace.
Tony Hwang
Calgary, AB
+1, control voltage is always present which is originating from thermostat Y terminal. Analog or digital thermostat? Trouble-shoot with multi meter.
WorthFlorida
6th clinical trail chemotherapy 5/15/24
Solutions
Orlando, Florida
If it was the thermostat the fans both inside and outside would be running. The outside contractor also turns on the condenser fan but some units l have a small circuit board if there is a two speed fan.
The control board inside the air handler probably went bad. You did blow a fuse. You need to trace back the wire from the compressor relay back to the air handler. Look for any burn marks on the control board. FYI 24v ac operates the contactor.
DonL
Houston, TX
Was the fuse that blew the one for the T-Stat transformer ?
If that voltage is missing the outside unit may run, But the inside blower may not.
Good Luck. Never use a bigger fuse.
With the thermostat off (i.e., not calling for cooling), double-check the voltage at the contactor's coil. If it has 24vac across it, double check it at the thermostat base. It should be open. without the thermostat in the circuit, if there's 24vac on the yellow to common, there's a short somewhere.
Essentially, the thermostat is just a smart switch...when cooling is called for, it connects the R to Y to supply voltage to the ac contactor (the return line is wired from the ac unit to the source of the 24vac). That turns the ac unit on. It may or may not immediately turn on the circulation fan.
IOW, you're looking for where the coil is getting 24vac when the thermostat is not calling for cooling. It could be a defective thermostat, a connection between the R and Y somewhere else, or a defective contactor, but that doesn't seem to be the case. But, if you miswired the contactor, it's possible it could be getting the coil energized, but it would be a weird set of circumstances.