    Redoing my camp plumbing. I’ve done some plumbing before but not an awful lot. I just want to make sure I do it right the first time. My question is with the drain plumbing. Does this diagram look like the system would work well? 49290187-6695-4688-A066-BE188B8F88E9.jpeg
     
  2. Ryan Miehm

    Ryan Miehm New Member

    Joined:
    Jan 20, 2020
    Location:
    Ontario
    here in Ontario, Canada, that set up would be fine.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. Ryan Miehm

    Ryan Miehm New Member

    Joined:
    Jan 20, 2020
    Location:
    Ontario
    drain from the 3" toilet line to the kitchen sink connection would need to be 2" as it would act as a wet went for the toilet.
     
  5. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    Okay. All of the rest would be ok with 1 1/2? Shower would be 2” as well?
     
  6. Ryan Miehm

    Ryan Miehm New Member

    Joined:
    Jan 20, 2020
    Location:
    Ontario
    here in ontario, this would work as well, having the kitchen and bathroom sink connected together with a double fixture fitting.
     

    Attached Files:

  7. Ryan Miehm

    Ryan Miehm New Member

    Joined:
    Jan 20, 2020
    Location:
    Ontario
    and as long as there is nothing draining into the vertical 3" stack above the shower, the shower will not need its own vent. and shower drain should be 2"
     
  8. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    Thank you! The shower will be the highest on the stack. Nothing above it.
     
  9. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    They allow a kitchen sink to wet vent in Canada? Not if it were in the US.
     
  10. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    I’m in Pennsylvania. I cannot connect the sink the way the diagram shows?
     
  11. Reach4

    Reach4 Well-Known Member

    Joined:
    Sep 25, 2013
    Location:
    IL
    Everybody would like this, I think: IMG_5.jpg
     
  12. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    Not where you live.
    Wet venting is for bathroom fixtures only.
    The lav can wet vent the toilet if it's run with 2".
    The kitchen sink comes in downstream of the toilet with it's own vent, which can tie in to the wc/lav vent at 42" above the floor.
     
  13. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    So the above diagram would work? Just have 2 seperate wyes in the horizontal? Also would the kitchen and the bath sink both be 2"?
     
  14. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    would this work?
    2CB8B96E-7407-4B79-AC4F-096701FFF989.jpeg
     
  15. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    The kitchen sink with 2" cleanout
    The lav run with 2" because it wet vents the toilet.
    Yes.
     
  16. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
    Thank you. Where would you suggest I put the clean outs? Should I put one on the closet flange if I have room? Also the wyes on the horizontal should be turned no more than 45 degrees? Also the santee on the top vent pipe should flow up or down? Thanks
     
  17. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    The kitchen sink needs it's cleanout, if you install a 3" there it would also handle the toilet. Somewhere you need a 3" near the end of the run.

    Vent santees are upside down.
     
  18. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
     
  19. Justin1987

    Justin1987 New Member

    Joined:
    Mar 24, 2020
    Location:
    Pittsburgh Pa
     
Similar Threads: Bathroom rough
Forum Title Date
Plumbing Forum, Professional & DIY Advice Basement Bathroom Rough-in with Sewage Ejector Pump Mar 25, 2020
Plumbing Forum, Professional & DIY Advice Help with basement bathroom rough in Mar 19, 2020
Plumbing Forum, Professional & DIY Advice Rough in Washer/Bathroom Feb 29, 2020
Plumbing Forum, Professional & DIY Advice The rough-in for this basement bathroom doesn’t look right to me. What do you think? Feb 9, 2020
Plumbing Forum, Professional & DIY Advice Wet venting and layout of rough in of new bathroom Nov 7, 2019

Share This Page