Basement closet wall with foam needs drywall for fireproof?

Users who are viewing this thread

lmei007

Member
Messages
183
Reaction score
0
Points
16
Location
Maryland
I have a closet in the basement. One of the walls has foam between the closet wall and the concrete wall. Do I have to put dry wall there for fire code?
 

Attachments

  • IMG_20160604_102834.jpg
    IMG_20160604_102834.jpg
    67 KB · Views: 560

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Yes, it needs to have a standard timed thermal barrier against ignition to meet code. Half inch gypsum board works.

Before you close it all up:

Are the seams in the foam panels air sealed with can-foam or caulk or something?

How thick is the foam?

How much of the foundation wall extends above grade?

Code min performance for foundations in most of MD (US climate zone 4A, except Garrett County, which is zone 5A) is R10 continuous insulation. While technically that could be met with 2" of blue XPS from a labeled-R point of view, it's long term performance is closer to R8.5. For at least the top half of the wall (down to a couple feet below grade) it's probably worth adding batt insulation even if it's 2" foam. If it's thinner than 2" adding batts is advised too. Only unfaced batts or kraft faced, not foil faced, and DON'T install interior side vapor retarders other than standard latex paint on the half-inch wallboard.

If there is any chance at all of a flood you may want to stop the batt insulation above the anticipated high-water mark.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
The boards are only 2' wide, so there are seams between adjacent panels. Those seams leak air unless sealed somehow, and sometimes that becomes a moisture problem. You can use 1 part expanding foam, or polyurethane caulk, or purpose made tapes. The top edge and bottom edge of the foam needs to be sealed too where it meets the slab and whatever is above. At the top of a foundation it's common to have a horizontal chunk of foam over the top of the foundation leading up to the foundation sill plate.

Rim%20joist%20insulation%20-%20BSC.jpg


At 2" it meets the letter of code for R-value but it's still worth adding batts to the top half of the wall. "Contractor roll" R13s are usually cheap enough to make that worthwhile.
 