Thank you in advance for your advice...
For a kitchen remodel I am replacing a range which is wired with a 50 Amp circuit an 6 AWG AL wire with a cooktop calling for a 30 Amp circuit and 20 Amp oven which will be installed below the cooktop.
I saw that the code allows these two to be wired on the same circuit, but has a description on how to wire it that I do not exactly understand. How would this connection look, can I join two 10/2 wires (or the pigtails from cooktop and oven) to the 6 AWG with some Polaris IPLG6-3B use them to wire up the two units?
The circuit breaker/fuse is there to protect the wiring, not the device. So, as I understand it, up to the entry of the devices, the wiring must be sized for the circuit involved unless the devices involved say otherwise.
Stuff
Pennsylvania
Plan is good if a 50 amp circuit as done all the time. Problem is 6 gauge AL is only good for 40 amps if NM or SE.
Exception No.1: Conductors tapped from a 50-ampere
branch circuit supplying electric ranges. wall-mounted
electric ovens, and counter-mounted electric cooking units
shall have an ampacity of not less than 20 amperes and
shall be sufficient for the load to be served. These tap conductors
include any conductors that are a part of the leads
supplied with the appliance that are smaller than the
branch-circuit conductors. The taps shall not be longer
than necessary for servicing the appliance.
SK78
Michigan
That is how I would have thought of it as well.
However, there is this reference in the code:
Table 220.55 in the NEC, footnote 4:
  1. Branch-Circuit Load. It shall be permissible to calculate the branch-circuit load for one range in accordance with Table 220.55. The branch- circuit load for one wall-mounted oven or one counter-mounted cooking unit shall be the nameplate rating of the appliance. The branch-circuit load for a counter-mounted cooking unit and not more than two wall-mounted ovens. all supplied from a single branch circuit and located in the same room, shall be calculated by adding the nameplate rating of the individual appliances and treating this total as equivalent to one range.
Also Rex Cauldwell in Wiring a House also refers to this and shows a diagram.
So it must be approved, my question then is with the AL wire, would the Polaris connector be permissible and the correct one for the application?
Stuff
Pennsylvania
Article 220 is not normally used for breaker or wire sizing. Read 220.40 - the section is used for the calculation to size feeders or service.
Good point: Those grey Polaris are for copper only. Polaris black connectors are listed for connecting both aluminum and copper wires. Have to be in a junction box, though.
https://www.polarisconnectors.com/pdfs/NSi/IPL_series.pdf
Norcal01
Is the existing circuit a 3-wire or 4-wire feed? If 3-wire you cannot extend it, new feeds will have to be run to comply current requirements, as the 3-wire feeds are only allowed in existing installations, as soon as changes are made it's no longer existing. See NEC art. 250.140
SK78
Michigan
you are correct Norcal, it is a 3-wire in a home built in 1997. Out of luck I guess. Do you know if there is a way to run a separate conductor to the kitchen rather then replacing the whole wire. Its up in a drop ceiling so I would like to avoid running that heavy 6/3 wire if possible.
It is not code compliant to run a separate ground wire to augment an existing cable. Now, if it were in a conduit using say separate conductions, yes, but not with an existing cable.
SK78
Michigan
OK, thanks Jim, I guess I will be wrestling an anaconda next weekend.
SK78
Michigan
One more question, my options to replace the wire are a 6/3 copper or an AL service wire from what I found. Can someone tell me what the correct AL wire designation is that I would need? Is it 6-6-6-6 SER?
Stuff
Pennsylvania
4-4-4-6 SER AL is good for 55 amps
6-6-6-6 SER Cu is good for 55 amps
6/3 NM-B Cu is good for 55 amps
8/3 MC/AC/THHN in conduit Cu is good for 50 amps
SK78
Michigan
Thank you!
I had another thought.
The induction cooktop calls for a 30AMP 3 wire circuit.
The new oven is a 20 AMP 4 wire circuit.
Could I use the existing 50 AMP 3 wire for the cooktop and run a new 20 AMP 12/3 for the oven?
Stuff
Pennsylvania
Repurposing the 6/2 and a running a separate 12/3 should work. The 6/2 would be hot, hot, and ground. You would then need two double pole breakers in your electrical panel.
Technically there might be an issue that the grounding conductor needs upsized. Rule is if the wire is upsized (installing 6 AL instead of needed 8) then you need to upsize the grounding wire proportionately. So if current cable is 6-6-6 you are good but if 6-6-8 it would fail.
Norcal01
Are the new appliances 120/240V or straight 240V? If they do not require a neutral things could be looking up.
BiG_Mackenzie
Texas
I am not an expert but a standard kitchen range with four burners and an oven could draw 30, 40, or 50 amps. However, I will advise you to watch the tech blogs where is written about these devices. Before buying something, I take a look all the time on hellodiya blog where you can find more useful information about ovens, washing machines, or other devices. It was a huge help for me when I changed all devices at my home. All works till now without any problems.