I would need to buy two of these, right? One for the two hot conductors and one for the fused neutral/ground? Would a 3-port work just as well?The Polaris in the bottom pic is rated 14-4 AWG.
I would need to buy two of these, right? One for the two hot conductors and one for the fused neutral/ground? Would a 3-port work just as well?The Polaris in the bottom pic is rated 14-4 AWG.
I think it would be important to center the holes into the studs. That has to be hard to get stuff aligned.That's good hearing! These are semi-custom KraftMaid cabinets, all plywood construction. Unbelievably, the printed installation instructions that came with the cabinets (and posted on the Kraft Maid website) say to drill 7/32" pilot holes into the studs to mount the wall cabinets using the supplied #9 cabinet screws, which are very similar to GRKs but have a larger head. Looking at the size of the drill bit, I was immediately skeptical, and I'm glad I drilled a test hole because the holes are way too big, and there is ZERO bite from the threads! The screw just falls into the hole.
Yes indeed! The screw holes from the previously installed cabinets are still in the wall. I am using those as a partial reference.I think it would be important to center the holes into the studs. That has to be hard to get stuff aligned.
No they don't work like that. All the ports are connected. The one in the pic has two ports connected together, the part on top with the rubber plugs is where the set screws are located. So you need 3 of the 2 port.I would need to buy two of these, right? One for the two hot conductors and one for the fused neutral/ground? Would a 3-port work just as well?
When you installed the GFCI breaker, did you move the bare neutral SE conductor to the neutral terminal on the breaker?So what should I do? What would you do?
That's not going to work, the circuit's neutral conductor has to terminate on the GFCI breaker, because the breaker has to monitor all the circuit conductors. If you don't do this, you get exactly the symptom you are having.As I recall, I connected both hot wires to the GFCI breaker and the pigtail to the neutral bus. I did not touch or modify the neutral SE conductor in any way (as you can see in the pic, it terminates on the neutral bus).
And as to a grounding strap, when the oven comes with a 4-wire whip like you have, that doesn't apply. The grounding is determined by how you connect those 4 wires.
Oh.... So the inspector didn't catch that? Ugh.That's not going to work, the circuit's neutral conductor has to terminate on the GFCI breaker, because the breaker has to monitor all the circuit conductors. If you don't do this, you get exactly the symptom you are having.
[I guess it would work if the circuit were straight 240V with no load on the neutral circuit conductor, although at that point you'd instead call that conductor an EGC, as discussed earlier in the thread.]
Cheers, Wayne
It's correct with or without a GFCI breaker. The oven is using the neutral conductor for bonding it's non-current carrying metal parts, which is usually not allowed, but there is an exception for existing branch circuit installations.The oven installation instructions for a 3-wire system show it as I have it currently wired: the neutral and ground wires from the oven are joined. I presume that is the correct method WITHOUT a GFCI breaker.
The oven's ground wire should be connected to the branch circuit neutral as you have done.But there is no alternate installation method, since I do not have a grounding conductor. If I disconnect the ground wire, there will be no return path if there is a ground fault, right? What am I missing?
That would be an issue for the GFCI to work properly (it could lead to tripping due to some of the neutral current not passing through the GFCI), but would not otherwise be a big deal.One last question: It looks like the bare stranded neutral is touching the SE neutral where it comes into the panel.
Here's what the 2023 NEC (not yet adopted in OR, I believe) says to do when using an existing SE cable that doesn't not originate in the service panel (a new allowance, that used to be prohibited for continued use):Besides trying to physically separate these wires, how do you recommend that I insulate them and prevent them from coming into contact? Would electrical tape be okay?