SanTee legal at 45?

Users who are viewing this thread

Greenmountain

Member
Messages
67
Reaction score
0
Points
6
Location
Colorado
I'm guessing this does not work, but since code considers 45 equal to verticle, would it then be legal to set a SanTee at 45? (All other aspects being normal/conventional in that the trap arm would come in horiz to a street 45 to the SanT, vent out the top through another street 45, and drain out the bottom.)
 

Greenmountain

Member
Messages
67
Reaction score
0
Points
6
Location
Colorado
wow, cool! I was thinking it seemed similar in configuration to trap arm into a wye; and I feel like I remember reading that (in CO at least) trap arms MUST drain into a SanTee, so thought maybe the 45 would break a literal interpretation of that?

Here's a pic to illustrate the arrangement I'm asking about...

45SanTee.jpg
 

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
Yeah, not allowed in that sense for a trap arm that needs venting. What would be allowed would be rotate the san-tee 45 degrees about the side entry, so it is still at 2% slope while the straight inlet and outlet are vertical at 100% (1:1) slope.

Cheers, Wayne
 

John Gayewski

In the Trades
Messages
4,424
Reaction score
1,382
Points
113
Location
Iowa
b/c the vent needs to be before trap arm drops down?
Yes. From inside of the pipe, if you were looking, you should be able to see the vent before the elevation changes enough to block it from view. UPC is more strict.
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,461
Points
113
Location
Bothell, Washington
Website
terrylove.com
You're allowed 2% grade, 1/4" per foot.
You're not allowed to use fittings and raise it at a crazy angle that defeats the purpose of venting.
 

wwhitney

In the Trades
Messages
6,592
Reaction score
1,858
Points
113
Location
Berkeley, CA
NOPE. the side inlet has to be horizontal, NOT vertical to be legal.
For drainage (both inlets are vented drains), all that matters is that the outlet is vertical. The only case where that rule differs from what you said is the configuration shown in the OP (if both inlets were vented drains).

Cheers, Wayne
 

Reach4

Well-Known Member
Messages
38,964
Reaction score
4,463
Points
113
Location
IL
I am not sure what you want to do, but would this do it for you?
img_3.jpg
 

Greenmountain

Member
Messages
67
Reaction score
0
Points
6
Location
Colorado
Tilting the SanT to 45 would have facilitated things given my framing, etc, but I can still do it with the SanT vertical, so question was kinda more just out of curiosity
Thanks for all the replies:)
 

Reach4

Well-Known Member
Messages
38,964
Reaction score
4,463
Points
113
Location
IL
The santee can tilt up to 45 degrees, but only in the plane where the trap arm is still horizontal.
 