See attached layout. A local plumber recommended venting this kitchen sink with an AAV (Air Admittance Valve), but I am not that familiar with these devices. I was going to tie it into the main stack vent to only have a single cutout in the roof, but this has a long up and down path thru the attic. Another option is a separate stack on its own, but this would be towards the front of the house which I want to avoid if possible. Any thoughts on this?

Thanks,

Scott
 

Attachments

  • Capture.JPG
    Capture.JPG
    78.9 KB · Views: 152

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
I have always had three or more vents through the roof. I've also not been allowed to angle up and then down with my vent.
 

wwhitney

In the Trades
Messages
6,567
Reaction score
1,847
Points
113
Location
Berkeley, CA
I've also not been allowed to angle up and then down with my vent.
That seems to be a difference between the UPC and the IPC. The UPC says ". . . vent shall be level or shall be so graded and connected as to drip back by gravity to the drainage pipe it serves." Which wouldn't allow the up and then down.

https://up.codes/viewer/california/ca-plumbing-code-2019/chapter/9/vents#905.0

But the IPC says "Vent and branch vent pipes shall be so graded and connected as to drain back to the drainage pipe by gravity." [Which precludes any level sections.] Since it doesn't specify the drainage pipe served by the vent, one can argue that the up and down is allowed, as each side connects to a vent that drains back to a drainage pipe.

https://up.codes/viewer/colorado/ipc-2018/chapter/9/vents#905.2

Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,945
Reaction score
2,232
Points
113
Location
92346
no up and down with vents. easiest is the aav im not googleing your zip code and guessing your plumbing code to know if its allowed.
so run a new stack or run aav.
 

John Gayewski

In the Trades
Messages
4,360
Reaction score
1,345
Points
113
Location
Iowa
Upc doesn't allow aav's. Being that your plumber advised you to use an aav I'm going to say your ipc.

To me this looks like an enlarged island vent. I don't think any inspector would disallow any option other than the aav (in the case of upc).

I would go with the individual stack mainly becuse it's easier than running all of that pipe through the attic in my opinion. Plus it's more sound and less likley to give you any differential pressure.
 

James23912

Member
Messages
110
Reaction score
7
Points
18
Location
Vermont
Could you run it along the attic floor to the smaller rear vent, giving a slight rise? Or using option 3, instead of going down, run it thru the roof near the peak on the back?
 

Jeff H Young

In the Trades
Messages
8,945
Reaction score
2,232
Points
113
Location
92346
I'm not a fan of AAV but I'm guessing there are literally millions in use and its legal there . but if all your walls are open and you haven't got a roof on just run a vent up and through roof its easy right?
 

Scott Yackley

New Member
Messages
15
Reaction score
2
Points
3
Location
48383
Thanks for all of the feedback. Thinking will add this vent thru the roof so it is done right and don't have to worry about a mechanical device (AAV) failing down the road.
 

Jeff H Young

In the Trades
Messages
8,945
Reaction score
2,232
Points
113
Location
92346
Thanks for all of the feedback. Thinking will add this vent thru the roof so it is done right and don't have to worry about a mechanical device (AAV) failing down the road.
yea that is best , especialy if dosent require ripping open a lot of walls
 

Reach4

Well-Known Member
Messages
38,892
Reaction score
4,436
Points
113
Location
IL
Thanks for all of the feedback. Thinking will add this vent thru the roof so it is done right and don't have to worry about a mechanical device (AAV) failing down the road.
Why not the inverted V? Are you thinking it is against your code, or you suspect it will not work well?

If you do go through the roof, you will probably involve a roofer. Plumbing vent flashing is like a special shingle.
 

Jeff H Young

In the Trades
Messages
8,945
Reaction score
2,232
Points
113
Location
92346
Why not the inverted V? Are you thinking it is against your code, or you suspect it will not work well?

If you do go through the roof, you will probably involve a roofer. Plumbing vent flashing is like a special shingle.
Maybe its not roofed or he is re roofing soon
 

DIYorBust

Active Member
Messages
753
Reaction score
94
Points
28
Location
Long Island, New York
I have read, possibly on this forum, that an up and then down vent pattern can cause the accumulation of lighter than air gasses at the top, methane perhaps? Can you vent it near the top and lower one branch?
 