If it stays that way, a csv wouldnt help. Only if other water us being used at the same time.
Other water use at the same time as the heat pump only helps to reduce cycling, not causes it.
For example, if your well pump supplied 12 GPM and your HP consumed 8 GPM, then 4-GPM will be flowing into the pressure tank. With the pressure tank becoming filled and the system pressure rising to the cut-out pressure, the pump will shut off.
If you were to use that 4 GPM that is flowing into the pressure tank, then the system pressure will not rise so the cutout pressure will not be achieved so the pump will run continuously with no cycling. If you were to use 3 of those 4 gallons, then only 1 GPM will flow into the PT so it will take significantly longer for the tank to become full, allowing the pump to run longer before the cut-out pressure is achieved.
Your current 85 gallon PT will hold approx 21 gallons only. Because the PT purpose is to reduce cycling, the usually recommended PT capacity will cause the pump to operate for between 60-120 seconds after there is no further water use.
Of course with both examples, the 21-gallons will be depleted quickly from the PT so the pump will activate fairly rapidly again after shut-off.
If your well pump is not cycling while only the HP is operating, that would signify the HP is consuming 100% of the well pump's capacity, leading to the question if the well pump is actually supplying sufficient flow to the HP, particularly while there is other water use occurring at the same time the HP is operating.
I dont see how amps used would drop.
Much of the time, the full GPM capacity for the pump will not be needed so a CSV will reduce the flow from the pump to match the actual flow rate needed. If your pump can deliver 12 GPM but you are only using 3 GPM for a shower, then you really don't need the remaining 9 GPM to fill the PT to cause the pump to cycle repeatedly for as long as water use continues.
As a simplified explanation, a 12 GPM capacity pump moving 12 GPM water will be working at full capacity and will therefore require the most electrical power. If that pump's flow rate is reduced by a CSV, although the pressure between the pump and CSV will rise, the actual quantity of water the pump is forced to move will be reduced. Since the pump will not need to move as much water, it will not need to work as hard, so it will therefore not need to consume as much electricity to maintain the same RPM.