That pump can build 560' of head which is the same as 242 PSI. To be able to set a CSV at 50 PSI the pump should build no more than 175 PSI. This means the static water level would need to be 155' or deeper for a single CSV1A to work.
However, we have system like this where the static level is 5' and the inlet pressure to the CSV will be 242 PSI. In these cases we use two of the CSV1A valves in series. The first one sees the 242 PSI coming in and is set at 150 PSI. The second CSV sees the 150 PSI from the first CSV and reduces it to the 50 PSI needed for the house and sprinklers. This way there is never more than 125 PSI across either CSV1A and they will last a long time. You just need well pipe that can handle the 242 PSI, which most well pipe can easily do.
Other than that you just need to double up on the number of sprinklers, or increase the sprinkler nozzle size. It is important without a CSV that the output of the sprinklers be the same as the output of the pump to eliminate cycling. However, you should also realize that when doing this you are using every drop the pump can supply, so if you turn on a shower while the sprinklers are running you will have to wiggle around to get wet.
This doesn't happen when using a CSV as the sprinklers do not have to max out the pump, and there is water left when needed in the house.