14 years I installed the water heater using copper pipe (no flex line) to dielectric unions installed on the water heater.



When I attempted to replace the water heater the unions were welded together. They came away from the heater ok but would not disassemble as designed; I had to cut the copper pipe. Even when taking the unions to the bench vice there was no separating them. They were heavily corroded.



I am endeavoring to prevent a repeat of this situation and want comments on my plan, which is;

[copper pipe] to [dielectric union] to [12" neoprene hose with 316 stainless steel fittings] to [water heater].



What I want to know is if this will eliminate the corrosion on the dielectric unions.
 

Reach4

Well-Known Member
Messages
38,857
Reaction score
4,427
Points
113
Location
IL
[copper pipe] to [dielectric union] to [12" neoprene hose with 316 stainless steel fittings] to [water heater].
You want corrugated stainless or copper connector lines -- not rubber with a metal braid. Click Inbox, above.

I don't know about whether dialectic unions would be helpful. I would guess not, but I am not sure.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
In California they use flex connectors and earthquake straps because of the earthquakes that they have. It's that way on the entire West Coast.

Water heaters come with dielectric nipples which work fine with flex connectors. I quit using the unions decades ago because they close off and prevent water flow.

rheem-gas-lomet.jpg


 
Last edited:

Shopco

Member
Messages
50
Reaction score
1
Points
6
Location
Riverside, CA
You want corrugated stainless or copper connector lines -- not rubber with a metal braid. Click Inbox, above.

I don't know about whether dialectic unions would be helpful. I would guess not, but I am not sure.
Why corrugated? Not challenging; seeking knowledge
 

Reach4

Well-Known Member
Messages
38,857
Reaction score
4,427
Points
113
Location
IL
Why corrugated? Not challenging; seeking knowledge
Doesn't degrade and put black bits into your hot water.
Usually larger ID, which helps lower turbulence, but is that enough to overcome the corrugation? I don't know.
 

Shopco

Member
Messages
50
Reaction score
1
Points
6
Location
Riverside, CA
Thank you Reach4 for your interest in my situation. Neoprene shedding: huh, I never thought of that.

Research indicates excellent resistance to heat and ozone. Pressure rating is nearly 2x needed. Possible hardening over time but that should not be a problem in my case since there will be no bends . What does raise a concern is its sensitivity to chlorinated water. I have not tested our chlorine concentration, but the city reports 0.46ppm average (not that tells me anything regarding its effect on neoprene).

As far as the flex connections you suggested, they do indeed look like high quality items however, I do not see them working in my case. There is only 12" between the 1" ball valve and the water heater. I have installed SS ¾" flex with a 360° loop as a temporary fix until I get sorted but it is causing a severe water hammer, necessitating closing down the ball valve to reduce velocity.

P.S. hose is McMaster-Carr item No. 5291K57
 

Dj2

In the Trades
Messages
2,611
Reaction score
258
Points
83
Location
California
Corrugated flex is code in CA. Rigid pipes are not.
I've been using copper corrugated connectors since 1976, which are code compliant. They come with 3/4" black washers, that easily last the life of the water heater. See Terry's picture.
They come inn different lengths. If you go from 1" you will need a reducer to 3/4".
 

JerryKrinock

New Member
Messages
2
Reaction score
0
Points
1
Location
San José, CA
I understand that the dielectric union is required when joining copper to steel because these are dissimilar metals. But if I connect from copper to a stainless steel flex, then to a steel nipple on the water heater, and the stainless steel flex looks like it has a brass nut on each end, that is a lot of dissimilar metals touching one another! Do I need a dielectric joint of some kind if using a stainless steel flex like this?

(I might be wrong, but I prefer a stainless steel flex to a copper flex because I think that, in general, stainless steel is stronger and more corrosion resistant than copper.)
 

Onokai

Member
Messages
128
Reaction score
11
Points
18
Location
Arcata,Ca
I have always used Corrugated flex as it is code in CA,
They work well last forever and we just had a 6.4 earthquake this week and my 80 gallon Rheem solaraid tank and 40 gallon Rheem made it thru great. Both are strapped in to wall and supports.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
The copper and the stainless corrugated flex connectors are dielectric on the ends. I normally use 24" flex so that I can make smooth bends.
The braided supplies break down on water heaters and people find little black specks in their hot water over time. The black rubber breaks down.

corrugated-wh-supply-01.jpg


The ends are dielectric. They last as long as the water heater.
The galvanized nipples that come with water heaters have plastic liners. I've been doing this for 50 years now. Are you trying to catch me on something that the plumbers and the manufacturers haven't thought of yet? Good luck with that.
I don't give legal advice, I'm not trained for that. I do give advice on a practice that I've been researching and doing for 50 years.

index.php


A new dielectric union above and one 4 years old below.

dielectric-union-4-years-old.jpg


One more reason we used corrugated supplies that have their own union.
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
A nice basic example of a water heater installation for the rest of the country, not the West Coast though.
We need earthquake strapping and flexible supply lines.

wh-install-bradfordwhite.jpg
 

Onokai

Member
Messages
128
Reaction score
11
Points
18
Location
Arcata,Ca
I really like the flex lines with lots of play as well. We have had two earthquakes in past 15 days a 6.4 and a 5.4 so they shook the place. My tanks are strapped down tight and lines are all flex with lots of play in them. The 80 solar tank goes into the 40 gal water heater so they are tied down well and the lines have flex between them.
 

Jeff H Young

In the Trades
Messages
8,884
Reaction score
2,214
Points
113
Location
92346
Flexes are code for us, but they are quick and easy, personally I've fixed many leaks at the flexes but they aren't that common and most tanks are in garages . I think they make a decent installation and would be good to use even if not required. We didn't used to be required to use flexes here and we did anyway.
 

wwhitney

In the Trades
Messages
6,556
Reaction score
1,841
Points
113
Location
Berkeley, CA
As to "flexes are a code requirement," is that spelled out anywhere, or just a common interpretation?

Looking at the California Plumbing Code (or the UPC more broadly), I see the explicit requirement for straps in 507.2 "Seismic Provisions." But the only thing I see that could be construed as requiring a flexible connector is 507.3.1 which says in part "he appliances and equipment shall be supported and shall be connected to the piping so as not to exert undue stress on the connections."

Which isn't explicit. You could argue that if the water heater and the pipes are both securely strapped to the same part of the structure, then they are going to move together, and there will be no "undue stress on the connections."


Cheers, Wayne
 

Jeff H Young

In the Trades
Messages
8,884
Reaction score
2,214
Points
113
Location
92346
Not sure Wayne I really like to know these technicalities for a fact and not just hearsay so I like that challenge.
 

John Gayewski

In the Trades
Messages
4,346
Reaction score
1,340
Points
113
Location
Iowa
Yeah I only ever remember reading that the water heater be strapped down.

I've read the whole UPC, but digesting it is another story. I think would will take more years of referencing it. It's amazing how many things I remember incorrectly or slightly distorted.
 

Jeff H Young

In the Trades
Messages
8,884
Reaction score
2,214
Points
113
Location
92346
Yeah I only ever remember reading that the water heater be strapped down.

I've read the whole UPC, but digesting it is another story. I think would will take more years of referencing it. It's amazing how many things I remember incorrectly or slightly distorted.
That's a major reason I like this site, I will say that on big jobs often spec out flex lines on plumbing or HVAC.
I found what bI call a screwup in CA plumbing code today going back to 2018 CPC and sediment traps on the gas lines requiring the gas flex be downstream of the dirt leg. don't know how many I did wrong but its changed now but I never know which codes are adopted. I've really had to figure this stuff out myself and some stuff I still haven't figured out
 