Greetings
Note: My LPG tank is full and my furnace is functioning properly with LPG
Takagi T-K3 LPG
The unit is I’m guessing 15 to 20 years old so it may be at its end ,but if there is a short quick fix - I am all ears
Trouble code: 111
Initially, while taking a shower ,the water temperature fluctuated from hot to cold & back to hot.
Looked in the owners manual under general troubleshooting and it recommended changing the inlet water filter, which I did; fired the unit up and had hot water & figured the problem was solved.
But Nooo…
2 days ago, took a shower and no hot water-not even fluctuation’s.
I then poked around on the Internet looking for information and then found the LED display after I took off the cover and it was showing “111”.
What I have done troubleshooting wise so far:
Pulled both the igniter and flame rods ,sandpapered rods and visually inspected: no cracks or chips in the ceramic bodies & the rods are tight in the bodies.
Checked for spark coming out of the ignition rod and am getting said spark.
The site glass window is grungy and am unable to clean,so I can’t see if there is an initial spark or flame.
When cycling, the fan turns on then the gas valve self tests-“clunkCLUNK-clunk-clunkCLUNK-clunk-clunkCLUNK-clunk”, then the fan RPMs will increase and the LED trouble code will be displayed.
Possibly a fuel supply issue as there’s air and spark but may be no fuel to complete the combustion.
Is that small then loud “clunk” with the gas valve normal?
I’m wondering if the gas valve is suspect(?)
Sooo…
That’s where I’m at;any recommendations and suggestions are greatly appreciated.
Thank you
Note: My LPG tank is full and my furnace is functioning properly with LPG
Takagi T-K3 LPG
The unit is I’m guessing 15 to 20 years old so it may be at its end ,but if there is a short quick fix - I am all ears
Trouble code: 111
Initially, while taking a shower ,the water temperature fluctuated from hot to cold & back to hot.
Looked in the owners manual under general troubleshooting and it recommended changing the inlet water filter, which I did; fired the unit up and had hot water & figured the problem was solved.
But Nooo…
2 days ago, took a shower and no hot water-not even fluctuation’s.
I then poked around on the Internet looking for information and then found the LED display after I took off the cover and it was showing “111”.
What I have done troubleshooting wise so far:
Pulled both the igniter and flame rods ,sandpapered rods and visually inspected: no cracks or chips in the ceramic bodies & the rods are tight in the bodies.
Checked for spark coming out of the ignition rod and am getting said spark.
The site glass window is grungy and am unable to clean,so I can’t see if there is an initial spark or flame.
When cycling, the fan turns on then the gas valve self tests-“clunkCLUNK-clunk-clunkCLUNK-clunk-clunkCLUNK-clunk”, then the fan RPMs will increase and the LED trouble code will be displayed.
Possibly a fuel supply issue as there’s air and spark but may be no fuel to complete the combustion.
Is that small then loud “clunk” with the gas valve normal?
I’m wondering if the gas valve is suspect(?)
Sooo…
That’s where I’m at;any recommendations and suggestions are greatly appreciated.
Thank you