Short radius 45's for

Users who are viewing this thread

yourlocalhandsyman

New Member
Messages
19
Reaction score
3
Points
3
Location
Ontario
Looking through the NPC 2020, it specifically states that short radius 90's cannot be used to connect 2 drainage pipes except in 2 very specific circumstances:

"90° Elbows
1) Except as permitted in Sentence (2), 90° elbows of NPS 4 or less whose centre-line radius is less than the NPS of the pipe shall not be used to join 2 sanitary drainage pipes.
2) For sanitary drainage systems of NPS 4 or less, 90° elbows described in Sentence (1) shall only be permitted a) to change the direction of piping from horizontal to vertical, in the direction of flow, b) where a trap arm enters a wall, or c) to connect trap arms as permitted by Sentence 2.5.6.3.(2)"

However, it says nothing about 45's and 22.5's. The issue is the local building centres in buttfuck nowhere literally don't carry medium/long sweeps, combos etc and take forever to get stuff in. Would an inspector pass using short radius/street short radius 45's going into wyes? Is there some place in the code I'm missing or is this just a sort of "best practices" rule?
 

yourlocalhandsyman

New Member
Messages
19
Reaction score
3
Points
3
Location
Ontario
1666755014822.png
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks