I have a symmetrical design (mirror image) for 2 bathrooms, where toilets, sinks clothes washer and bath tub are "back to back".
I want to follow the Canadian plumbing code.
I have attached a drawing with 3D view of the circuit, and a top view.
+ The green lines in the drawing represent wet vents.
+ The fat pipes have 3" diameter and the thin ones have 2" diameter.
Canadian code Table 2.5.8.1 (Max Hydraulic loads drained into a wet vent)
Wet Vent #1
+ serves 2 toilets, load = 8 f.u.
+ receives drainage of 3 f.u. (the two sinks) (OK with Table 2.5.8.1)
Wet Vent #2
+ serves 2 bathtubs, load = 3 f.u.
+ receives drainage of 4 f.u. (the two clothes washers) (OK with Table 2.5.8.1)
Trap arm lengths in the design:
+ toilets: 6'
+ bathtubs 7'
The Canadian code has a max length of 3.6m (11.8 feet) for 3" pipes and 2.4m (7.8 feet) for 2" pipes.
I have a symmetrical design (mirror image) for 2 bathrooms, where toilets, sinks clothes washer and bath tub are "back to back".
I want to follow the Canadian plumbing code.
I have attached a drawing with 3D view of the circuit, and a top view.
+ The green lines in the drawing represent wet vents.
+ The fat pipes have 3" diameter and the thin ones have 2" diameter.
Canadian code Table 2.5.8.1 (Max Hydraulic loads drained into a wet vent)
Nominal Pipe Size | Not serving Water Closet | Serving not more than 2 water closets |
2" | 4 | 3 |
Wet Vent #1
+ serves 2 toilets, load = 8 f.u.
+ receives drainage of 3 f.u. (the two sinks) (OK with Table 2.5.8.1)
Wet Vent #2
+ serves 2 bathtubs, load = 3 f.u.
+ receives drainage of 4 f.u. (the two clothes washers) (OK with Table 2.5.8.1)
Trap arm lengths in the design:
+ toilets: 6'
+ bathtubs 7'
The Canadian code has a max length of 3.6m (11.8 feet) for 3" pipes and 2.4m (7.8 feet) for 2" pipes.