Required pipe size based on W.S.F.Us

Users who are viewing this thread

Cyphie

New Member
Messages
15
Reaction score
1
Points
3
Location
NH
I am building a house served by a well. The well pump cycles on at 40 and off at 60 psi. As I read Appendix P of the 2018 IRC which governs the area I am building in, paragraph AP201.1 2 states "Obtain the minimum daily static service pressure [psi (kPa)] available (as determined by the local water authority) at the water meter or other source of supply at the installation location." Based on that what static pressure do I use when calculating pipe sizes? If I use the low 40 and subtract out height losses I am starting at 31 psi. This seems like the wrong starting point.

So, with more research, I think I figured it out. Since I am using a well, I should use pressure loss across the system to calculate pipe size.
 
Last edited:

Breplum

Licensed plumbing contractor
Messages
1,971
Reaction score
801
Points
113
Location
San Francisco Bay Area
I have no experience with wells, but I would use the chart related to 30 psi static since that is your worst case operating pressure unless you also have a pressure vessel or CSV.
 

Cyphie

New Member
Messages
15
Reaction score
1
Points
3
Location
NH
I have no experience with wells, but I would use the chart related to 30 psi static since that is your worst case operating pressure unless you also have a pressure vessel or CSV.
Thanks for the input. I found an interesting link that specifically discusses wells. Conducting the calculations with this method yielded similar results but was a bit less restrictive when it came to determining WFSUs allowed with longer runs of piping. https://dsps.wi.gov/Documents/Programs/Plumbing/SBD8036P_SizingWaterSupply.pdf
 

Jeff H Young

In the Trades
Messages
8,962
Reaction score
2,237
Points
113
Location
92346
its expected to use a 3/4 pipe all the way to a 3/4 x1/2 90 at the stub out if it sizes out to 3/4 pipe
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks