Hi there, I am doing a kitchen remodel and would like some inputs into best option for plumbing the new sink. To help me sort through my thoughts I came up with the following sketch. I am thinking that I have three options. I am leaning towards Option 1 since it is easiest and makes sense to me since I have a vent upstream the the previous sink wyed into. Thoughts? I live in NH and my city (Nashua) adopted IPC 2000.
EDITED:
This venting is not allowed to go horizontal below 6 inches above the flood level of the kitchen sink. You pretty much will need an AAV.
With AAV, I think #1 is OK under IPC if you increase the pipe pipe size to the stack . Ideally add a cleanout above or below the sanitary tee, but the trap adapter at the wall may be sufficient cleanout.
A kitchen sink is 2 DFUs, and IPC allows a 1.5 inch pipe to carry 3 DFUs. Maybe you should increase the pipe in the floor to 2 inch downstream.
wwhitney
Berkeley, CA
Are there any fixtures flowing into the 2" horizontal drain from the right side of the picture? If so, what?
Cheers, Wayne
rjking2112
Cheers, Wayne
Nothing to the far right but there is a input for a Saniflow up flow pump in the basement for a kitchenette sink that would tie in upstream of where I want to come down from the new sink on the first floor. That’s it.
rjking2112
EDITED:
Do you mean I need to increase the 2” horizontal drain?
I had missed that was a 2 inch drain under the floor. Your drawing was clear.
A 2-inch shared drain line below the floor may be sufficient after you add up the loads.
rjking2112
Ok great. Looks like I have 6 DFU (2 sinks and the tub upstairs) so I think I’m at the max for 2”. Thanks for your help.