Hi,
I live in England, where it is rare for people to have a private well water supply. One consequence of this is that there are not many companies around who have a lot of knowledge about boreholes for private house water supplies, and I have been really struggling to get good advice. I've read a lot on this forum and it's clear that there are some very knowledgeable and experienced people here, so after having struggled for well over a year to get a good, working, borehole system I'd like to describe my proposed system and hopefully explain why I want to change things. I wish I were as lucky as you folk in the US, where it seems having a well water supply is pretty normal, rather than the rarity it is here in England. Please excuse the units, we're metric here but I'll try and convert to US units to make things easier to understand where I can. I also apologise for this being a long first post, but thought it'd help if I tried to give as much background as possible.
Our borehole was drilled through 40m (around 130 ft) of hard clay, then through a few metres of running greensand (where the aquifer is) and then down into the underlying sandstone. The total drill depth was 65m (~ 212ft). The drill job was not a good one, and the drillers didn't know they had hit water, as they were wet drilling with polymer mud and the black clay coming up into the settling tanks was making it hard to see what they were drilling through. We were going to abandon the hole as being dry when one driller decided to come back the next day to test pump it and found we had a yield of at least 4,000 litres per hour (about 1000 US gallons per hour), with only a few metres drop in level after pumping for a couple of hours.
We decided to line the hole and use it, so dropped in 15m (~50 ft) of 125mm (~5 inch) OD perforated PVC screen, with a cap on the bottom, followed by 125mm liner to the well head. The lower 25m (~80ft) or so of the space around the lining was packed with graded crushed glass as filter pack, then the remainder of the liner was sealed to the bored hole with bentonite, to stop surface water running down. A concrete cap and manhole cover was fitted on the top to cover the well head. A Grundfos SQ1-65 pump was lowered in to 45m (~ 146 ft)down, so 20m (~65 ft) off the bottom. The rest water level in the hole is around 3.5m (~11 ft) from the surface.
The first problem (I know now, but didn't a year ago) is that the driller didn't develop the well, but left it. It sat unused while we built a new house. After around 6 months I connected up the pump and started checking the well out. The pump would easily pump 1400 litres per hour (about 370 US gals/hour) for days on end, with the water level in the well dropping to around 12m from the surface (so a drop of about 25 to 30 ft from the rest water level). I pumped the well hard like this for a couple of weeks, at the recommendation of the driller, but it kept pumping lots and lots of greensand.
I pulled the pump up, extended the pipe and cable and tried lowering it further, but found it wouldn't go down at all, it hit what we think is hard-packed sand, right below where the pump was sat (so the bottom 20m (~ 65ft) of the well is filled with packed sand. The driller came back to pull the pump out and try and airlift the sand out, but it was too solid to shift. He suggested I pull the pump up, as the water level is always high. I raised the pump by 20m (~65ft) and as long as I don't pump hard I get clean water, far more than I need to run the house, so I'm going to leave the well as it is, even though is has sand in the bottom, and maybe revisit the well problem later.
The water analysis showed we had hard water, pH around 8, TDS around 380 with a moderate iron content and a tiny bit of stinky Hydrogen Sulphide. The drillers knew nothing about filtration or treatment, so I was on my own. I found a pretty good filter system that works well, and uses a sand/Aquamandix media and an air pocket at the top with a spray to oxidise incoming water before it flows down through the filter. This does a great job at getting the iron and hydrogen sulphide out and the water only needs fine filtering, UV sterilisation and softening to be really nice. The filter, steriliser and softener all work fine, with no problem.
The iron filter needs a high backwash flow rate (around 30 litres/min, or ~ 8 US gallons a minute) If I pump this hard from the well I draw up sand after ten minutes or so. To stop the pump from drawing sand I need to keep the flow rate down below 10 litres/min (~2.6 US gal/min). The drillers suggested I fit a break tank, fill the break tank with water from the pump, with a restrictor to keep the flow rate down, then use a second pump to charge the pressure tank and run the house supply drawing from the break tank. This works fine, but is pretty complicated and takes a lot of space up. I have a 650 litre (~170 US gal) break tank, with a float switch, plus a 1hp pump and a 300 litre (~80 US gal) pressure tank, just so I can backwash the iron filter. Apart from taking up a load of space, I have to protect the external break tank from freezing in winter and have the noise of the 1hp supply pump (basements are rare in British houses, so the pump and filter is in a small shed on the side of the house).
I'd like to make the system a bit simpler, and work on just the borehole pump. That can deliver loads of pressure, but has to be restricted to 10 litres/min so that it doesn't draw up sand (which is OK, it's about what the shower uses, and that's the biggest water draw we have). I have room for a second 300 litre pressure tank in the shed, so am thinking of the following system, to get rid of the break tank and the second pump.
Keep the restrictor in the borehole pump and feed it direct to two 300 litre pressure tanks in parallel, charged to 5 bar, so basically two 80 US gal pressure tanks running at about 74 psi max. The filter back flush takes 8 minutes at 30 litres/minute maximum (from the spec sheet, it actually seems to draw about 26 litres/min on back flush, measured). I reckon that, with the pump kicking in to deliver 10 litres/min, plus the usable reserve of around 200 litres in the two pressure tanks, that should be OK for the back flush requirement (this is based on my calcs of the drawn down volume and pump switch on point), The first question is, does this sound like a sensible think to do?
From my perspective, if it would work OK, then it has a load of advantages. I can get rid of the big break tank and get rid of the 1hp second pump. I can simplify the wiring so that the borehole pump is just switched from the pressure switch. The system will be a lot quieter (except when doing a short backwash) as I no longer have the extra 1hp pump. There seems less to go wrong if I just have the pressure tanks, pressure switch, borehole pump and filter system.
In case the above isn't enough detail, the iron/H2S filter is a 1252 vessel with a Clack WS1 head and an air draw kit, designed and set up to have an air bubble at the top in use. It's big for our needs (we use around 250 litres/day, about 66 US gals a day), and we have it set to back wash every three days, which seems fine for keeping the iron levels well down and getting rid of the H2S. We have a 5 micron pleated polyester filter after this, then a UV steriliser (sterilisation is mandatory here, even though the water tested clear for bacteria). The softener is inside the house, a Harvey unit that works very well. We run the water system at 5 bar (~74 psi) right up to other side of the softener, then have a pressure reducing valve that drops the house supply down to 2.5 bar (about 37 psi). I've done this so that variations in pressure vessel pressure between pump on and off and the slight pressure losses through the filters etc, don't show up on the house supply.
Sorry this is a long post, I guess what I'm really looking for is just either confirmation that I'm on the right track, or being told I have it wrong and should just leave things as they are.
I have an additional question about sterilisation, but it seems rude to add that along with the above lengthy post.
Many thanks in advance for your patience in having read this far.
Jeremy
I live in England, where it is rare for people to have a private well water supply. One consequence of this is that there are not many companies around who have a lot of knowledge about boreholes for private house water supplies, and I have been really struggling to get good advice. I've read a lot on this forum and it's clear that there are some very knowledgeable and experienced people here, so after having struggled for well over a year to get a good, working, borehole system I'd like to describe my proposed system and hopefully explain why I want to change things. I wish I were as lucky as you folk in the US, where it seems having a well water supply is pretty normal, rather than the rarity it is here in England. Please excuse the units, we're metric here but I'll try and convert to US units to make things easier to understand where I can. I also apologise for this being a long first post, but thought it'd help if I tried to give as much background as possible.
Our borehole was drilled through 40m (around 130 ft) of hard clay, then through a few metres of running greensand (where the aquifer is) and then down into the underlying sandstone. The total drill depth was 65m (~ 212ft). The drill job was not a good one, and the drillers didn't know they had hit water, as they were wet drilling with polymer mud and the black clay coming up into the settling tanks was making it hard to see what they were drilling through. We were going to abandon the hole as being dry when one driller decided to come back the next day to test pump it and found we had a yield of at least 4,000 litres per hour (about 1000 US gallons per hour), with only a few metres drop in level after pumping for a couple of hours.
We decided to line the hole and use it, so dropped in 15m (~50 ft) of 125mm (~5 inch) OD perforated PVC screen, with a cap on the bottom, followed by 125mm liner to the well head. The lower 25m (~80ft) or so of the space around the lining was packed with graded crushed glass as filter pack, then the remainder of the liner was sealed to the bored hole with bentonite, to stop surface water running down. A concrete cap and manhole cover was fitted on the top to cover the well head. A Grundfos SQ1-65 pump was lowered in to 45m (~ 146 ft)down, so 20m (~65 ft) off the bottom. The rest water level in the hole is around 3.5m (~11 ft) from the surface.
The first problem (I know now, but didn't a year ago) is that the driller didn't develop the well, but left it. It sat unused while we built a new house. After around 6 months I connected up the pump and started checking the well out. The pump would easily pump 1400 litres per hour (about 370 US gals/hour) for days on end, with the water level in the well dropping to around 12m from the surface (so a drop of about 25 to 30 ft from the rest water level). I pumped the well hard like this for a couple of weeks, at the recommendation of the driller, but it kept pumping lots and lots of greensand.
I pulled the pump up, extended the pipe and cable and tried lowering it further, but found it wouldn't go down at all, it hit what we think is hard-packed sand, right below where the pump was sat (so the bottom 20m (~ 65ft) of the well is filled with packed sand. The driller came back to pull the pump out and try and airlift the sand out, but it was too solid to shift. He suggested I pull the pump up, as the water level is always high. I raised the pump by 20m (~65ft) and as long as I don't pump hard I get clean water, far more than I need to run the house, so I'm going to leave the well as it is, even though is has sand in the bottom, and maybe revisit the well problem later.
The water analysis showed we had hard water, pH around 8, TDS around 380 with a moderate iron content and a tiny bit of stinky Hydrogen Sulphide. The drillers knew nothing about filtration or treatment, so I was on my own. I found a pretty good filter system that works well, and uses a sand/Aquamandix media and an air pocket at the top with a spray to oxidise incoming water before it flows down through the filter. This does a great job at getting the iron and hydrogen sulphide out and the water only needs fine filtering, UV sterilisation and softening to be really nice. The filter, steriliser and softener all work fine, with no problem.
The iron filter needs a high backwash flow rate (around 30 litres/min, or ~ 8 US gallons a minute) If I pump this hard from the well I draw up sand after ten minutes or so. To stop the pump from drawing sand I need to keep the flow rate down below 10 litres/min (~2.6 US gal/min). The drillers suggested I fit a break tank, fill the break tank with water from the pump, with a restrictor to keep the flow rate down, then use a second pump to charge the pressure tank and run the house supply drawing from the break tank. This works fine, but is pretty complicated and takes a lot of space up. I have a 650 litre (~170 US gal) break tank, with a float switch, plus a 1hp pump and a 300 litre (~80 US gal) pressure tank, just so I can backwash the iron filter. Apart from taking up a load of space, I have to protect the external break tank from freezing in winter and have the noise of the 1hp supply pump (basements are rare in British houses, so the pump and filter is in a small shed on the side of the house).
I'd like to make the system a bit simpler, and work on just the borehole pump. That can deliver loads of pressure, but has to be restricted to 10 litres/min so that it doesn't draw up sand (which is OK, it's about what the shower uses, and that's the biggest water draw we have). I have room for a second 300 litre pressure tank in the shed, so am thinking of the following system, to get rid of the break tank and the second pump.
Keep the restrictor in the borehole pump and feed it direct to two 300 litre pressure tanks in parallel, charged to 5 bar, so basically two 80 US gal pressure tanks running at about 74 psi max. The filter back flush takes 8 minutes at 30 litres/minute maximum (from the spec sheet, it actually seems to draw about 26 litres/min on back flush, measured). I reckon that, with the pump kicking in to deliver 10 litres/min, plus the usable reserve of around 200 litres in the two pressure tanks, that should be OK for the back flush requirement (this is based on my calcs of the drawn down volume and pump switch on point), The first question is, does this sound like a sensible think to do?
From my perspective, if it would work OK, then it has a load of advantages. I can get rid of the big break tank and get rid of the 1hp second pump. I can simplify the wiring so that the borehole pump is just switched from the pressure switch. The system will be a lot quieter (except when doing a short backwash) as I no longer have the extra 1hp pump. There seems less to go wrong if I just have the pressure tanks, pressure switch, borehole pump and filter system.
In case the above isn't enough detail, the iron/H2S filter is a 1252 vessel with a Clack WS1 head and an air draw kit, designed and set up to have an air bubble at the top in use. It's big for our needs (we use around 250 litres/day, about 66 US gals a day), and we have it set to back wash every three days, which seems fine for keeping the iron levels well down and getting rid of the H2S. We have a 5 micron pleated polyester filter after this, then a UV steriliser (sterilisation is mandatory here, even though the water tested clear for bacteria). The softener is inside the house, a Harvey unit that works very well. We run the water system at 5 bar (~74 psi) right up to other side of the softener, then have a pressure reducing valve that drops the house supply down to 2.5 bar (about 37 psi). I've done this so that variations in pressure vessel pressure between pump on and off and the slight pressure losses through the filters etc, don't show up on the house supply.
Sorry this is a long post, I guess what I'm really looking for is just either confirmation that I'm on the right track, or being told I have it wrong and should just leave things as they are.
I have an additional question about sterilisation, but it seems rude to add that along with the above lengthy post.
Many thanks in advance for your patience in having read this far.
Jeremy