skikt22
New Member
I have a question on PRV (pressure reducing valve, not relief ) performance and set-up
My situation: From Street to water heater
Street water pressure 160 to 180 psi
Wilkins 1 inch strainer- Put in as we used to have lots of rust,etc in the system. Street mains have since been replaced and this is probably no longer needed.
First PRV - Wilkins 1 inch BR4 set to 100psi
- This one supplies several outside taps and landscaping and then feeds the inside.
Second PRV - Wilkins 1 inch 600 set to 65 psi which feeds the inside of the house.
Watts expansion tank 4.6 gallon in front of water heater.
All internal plumbing is 3/4 inch - two hot and cold lines servicing different parts of the house. off the 1 inch and water heater.
My first question is how long the PRV should be expected to last. I do fairly regular maintenance of cleaning the screens but it seems that I end up with a failure about every three years on the Wilkins 600. My water heater relief valve blew again this weekend because the reducing valve has failed again, the last time it failed was just over three years ago. The spring was slightly corroded and the cap that goes on top of the spring had a lot of accumulated deposit on it that I was unable to get off. The diaphram looks ok, but I'm not sure what a bad one would look like. It seems three years is very short. Should I be replacing this PRV with a different brand like watts? Or did I just get a lemon on the first one. I know there are rebuild kits but they seem to be almost the price of a new valve and not readily available, and replacing the whole valve takes a lot less time.
The second question is about the amount of pressure drop I should get on the PRV's. When I run a faucet (2.5 gpm) the Wilkins 600 shows a drop of 5-10 psi (after I replaced it) which seems reasonable, but the BR4 shows a drop all the way to 40-50psi from 100. We have pressure drop off at times and I believe this is the cause. Is this an indication that it needs to be replaced or overhauled as well?
I also noticed one instance of street pressure after the first PRV which may just have been because I was fiddling with the system and could have had some momentary debris or it could be a early warning sign.
My situation: From Street to water heater
Street water pressure 160 to 180 psi
Wilkins 1 inch strainer- Put in as we used to have lots of rust,etc in the system. Street mains have since been replaced and this is probably no longer needed.
First PRV - Wilkins 1 inch BR4 set to 100psi
- This one supplies several outside taps and landscaping and then feeds the inside.
Second PRV - Wilkins 1 inch 600 set to 65 psi which feeds the inside of the house.
Watts expansion tank 4.6 gallon in front of water heater.
All internal plumbing is 3/4 inch - two hot and cold lines servicing different parts of the house. off the 1 inch and water heater.
My first question is how long the PRV should be expected to last. I do fairly regular maintenance of cleaning the screens but it seems that I end up with a failure about every three years on the Wilkins 600. My water heater relief valve blew again this weekend because the reducing valve has failed again, the last time it failed was just over three years ago. The spring was slightly corroded and the cap that goes on top of the spring had a lot of accumulated deposit on it that I was unable to get off. The diaphram looks ok, but I'm not sure what a bad one would look like. It seems three years is very short. Should I be replacing this PRV with a different brand like watts? Or did I just get a lemon on the first one. I know there are rebuild kits but they seem to be almost the price of a new valve and not readily available, and replacing the whole valve takes a lot less time.
The second question is about the amount of pressure drop I should get on the PRV's. When I run a faucet (2.5 gpm) the Wilkins 600 shows a drop of 5-10 psi (after I replaced it) which seems reasonable, but the BR4 shows a drop all the way to 40-50psi from 100. We have pressure drop off at times and I believe this is the cause. Is this an indication that it needs to be replaced or overhauled as well?
I also noticed one instance of street pressure after the first PRV which may just have been because I was fiddling with the system and could have had some momentary debris or it could be a early warning sign.