New floor drain - vent questions

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by MF41, Jul 8, 2012.

  1. MF41

    MF41 New Member

    Joined:
    Jul 8, 2012
    Location:
    PA
    Hi all,

    I would like to add a 6" floor drain with a 2" fitting to an existing cement floor in a small (15'x30') 2 story workshop building.

    I have a 3" main line running close by (about 12" but could be more or less if needed) to the location of the new drain. How can I vent this drain "easily" I believe I do need to vent? I'm also not sure how deep line is buried below the floor.

    The only thing upstream from this is a toilet (which looks to be on a sanitary tee and the vent line continues up.) The only thing downstream is a double laundry tub that is vented to up above the toilets location.

    Can anyone give any pointers?

    Thank you in advance.
     
  2. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    If I were to install a floor drain on a 3" line, it would need a 2" p-trap and have a vent before it entered the 3x2 wye. For sure if a toilet is on the line it will need the vent.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    Without being there it is impossible for us to tell you HOW to vent the drain, but it will probably NOT be an "easy way".
     
  5. MF41

    MF41 New Member

    Joined:
    Jul 8, 2012
    Location:
    PA
    Can I tap into the existing vent line for the sink or will I have to run a new vent line and connect it above the level of the toilet?
     
  6. Terry

    Terry Administrator Staff Member

    Joined:
    Aug 17, 2004
    Occupation:
    Plumber
    Location:
    Bothell, Washington
    A new vent is installed and can be revented above the toilet. We normally figure on 42" above the floor. That puts it 6" above a counter top, which would be the normal flood level.
     
Similar Threads: floor drain
Forum Title Date
Plumbing Forum, Professional & DIY Advice Reroute first floor toilet drain, reconnect existing 3" stack Apr 10, 2017
Plumbing Forum, Professional & DIY Advice Can I cover floor drain in 2nd fl bathroom? It's pretty useless. Apr 9, 2017
Plumbing Forum, Professional & DIY Advice Proper method for piping existing floor drains Apr 4, 2017
Plumbing Forum, Professional & DIY Advice Relocated Toilet Drain Directly Above 2x10 Floor Joist Feb 7, 2017
Plumbing Forum, Professional & DIY Advice Floor drain for softener Jan 29, 2017

Share This Page