Hi all-
Looking for a bit of confirmation here before I start ripping into walls/floors.
I'm splitting an existing bedroom into a new bedroom/bathroom. Layout is very limited with odd wall heights and sloped ceilings- this is really the only fixture layout that works. I'm going to be working with a plumber but doing all the demo/carpentry myself and I need a good plan in place before I begin the demo and wall construction.
The 3" stack is new, and this is really the only location it can go due to whats on the first floor.
My main question is the vent for the toilet- I'm seeing some rules are 5' and some rules are 6' max from 3" toilet drain to the vent. I'm at 5 1/2'. Is this OK?
The blue vent lines are midway up the wall and will tie into the stack above the drain connections of course. I'm assuming I'll have to build the wall out of 2x6's in order to cut a horizontal 2"vent line into the studs.
Floor joists are 2x8 so I hope to fit that toilet drain in there with a 90 off the flange. Below the entire bathroom is a first floor ceiling so I have to stay within that 2x8 joist bay.
Any criticisms in what I'm showing?
Looking for a bit of confirmation here before I start ripping into walls/floors.
I'm splitting an existing bedroom into a new bedroom/bathroom. Layout is very limited with odd wall heights and sloped ceilings- this is really the only fixture layout that works. I'm going to be working with a plumber but doing all the demo/carpentry myself and I need a good plan in place before I begin the demo and wall construction.
The 3" stack is new, and this is really the only location it can go due to whats on the first floor.
My main question is the vent for the toilet- I'm seeing some rules are 5' and some rules are 6' max from 3" toilet drain to the vent. I'm at 5 1/2'. Is this OK?
The blue vent lines are midway up the wall and will tie into the stack above the drain connections of course. I'm assuming I'll have to build the wall out of 2x6's in order to cut a horizontal 2"vent line into the studs.
Floor joists are 2x8 so I hope to fit that toilet drain in there with a 90 off the flange. Below the entire bathroom is a first floor ceiling so I have to stay within that 2x8 joist bay.
Any criticisms in what I'm showing?