Jeff H Young
In the Trades
Good info on the dry vent Wayne. One thing to be aware of with UPC code on dry vents is that a grey area of allowing vents horizontal below flood level can be done where structural condition require some specific wording but there are case where a horizontal dry vent below flood level is allowed.A dry vent takeoff can't be flat, it has to be taken off at a rise of at least 45 degrees above horizontal. So the takeoff is near the wall in order for the vent to be able to rise into the wall without going horizontal at all.
As to whether you can rise a little, then turn horizontal below the slab, and then turn up into the wall, in the US that depends on which plumbing code you are under. So you would need to check your plumbing code.
Cheers, Wayne
I don't see this as a case for allowing it flat just saying it can and is done legally with inspector approval