    Navien NPE 240A— Navilink recirculation—some customer insights.



    I have had The Navien NPE240A for about two years now and the unit has worked flawlessly, but it has taken me a while to get my recirculation settings working and recirculation parameters dialed in.

    I thought I would share here some of the things I have learned in the hopes it may help others as they consider this system. I welcome any comments or corrections.

    I was interested in this system because it seemed to offer the most control through their Navilink app, and the ability to control scheduled recirculation.

    I have an older home so a dedicate recirculation line was not an option for me. I am currently set up to recirculate warm water through to my farthest fixture using the cold-water line as a return. I recently upgraded from A Grundfos bypass valve to Naviens’ “Navicirc” bypass valve which I believe has a better flow and a higher closing temp.


    Some things to know before your buy:

    I chose the NPE240A because of its internal tank to provides a small reservoir of instantly hot water. During a recirculation cycle I don’t think this makes much of a difference because the water lines in my home are effectively the water tank. Off recirculation, on demand, this may help.

    In new construction I believe that a dedicated recirculation line to the farthest fixture is the way to go. Using the cold-water lines as the return limits how high the initial temperature can be at the farthest fixture. The Navicirc bypass closes at 95 degrees. This is an effort to not make the cold-water lines too hot. With a dedicated recirculation line, I believe the temperature can be as you set it. I do not at all mind having warmer water in the cold lines during recirculation. While I guess some of that warm water could be going down the toilet, in my household the recirculation times are mainly shower times.

    Navien makes it clear that they will only provide warranty support to units installed by their licensed contractors. While I have tackled many DIY projects this combination of plumbing, gas and venting was clearly best left to a qualified installer. Be careful that your installer has experience with these units. I live outside D.C. and used “Tankless Concepts”. Tankless heaters are all they do. They did a great job for me.

    Navien does not make clear the difference between scheduled recirculation and their “Hot Button”. The hot button ( in the navilink app)does a short recirculation cycle when you hit it bringing hot water to the farthest fixture.(there is also an option for a hard wired hot button) The Navilink app is software based for both IOS and Android. It communicates with their “Navilink” device. The app and the Navilink communicate either CAT5 wired or wirelessly to your router through you homes WIFI setup. The Navilink then controls your NPE. You can set a schedule on the app to tell your unit when to recirculate water through your lines. The scheduler controls the recirculation only. There is a separate switch which can shut down the unit if needed.

    The hot button is different. Even though it uses the same app. The hot button requires installation of a circuit board into the unit. When the hot button is activated scheduling is disabled. You can not have both. This does not make a lot of sense to me. Ideally, I would like to have a schedule in the morning and then be able to use a hot button later in the day if needed off schedule. I see no reason that the app could not incorporate a software based hot button and I have suggested this to Navien.

    There is however a work around… If you disable the scheduler in the app a recirculation cycle will begin. But you must remember to turn it back on again or your device will continue to recirculate.


    My biggest problem over most of my first two years of use was getting the scheduler to work and it came down to a simple issue. There is a button on the app for the weekly scheduler that says “enable” I would set the schedule and hit the enable button. What I recently learned is that the schedule is on when the button says “enable” and off when it says “disable”. Is should read “enabled/disabled” This is a Korean app developer language issue. I have notified Navien of this as well and I see that it has confused many others as well.

    My second biggest issue has been optimizing recirculation parameters. For recirculation Navien is not clear as to the use of parameters. There is always an interval between when water is called for and the start of the burner. During this delay gases are blown out of the exhaust and cold-water flows through the burner unheated leading later to a cold-water sandwich. I hoped that tweaking the parameters might mitigate this effect.

    Follow me here….and I think this is only relevant for those who use the cold system to recirculate. I can’t stop a cold-water flow at initial start up of the burners, but I hoped that by tweaking the parameters I might regulate the temperature of my pipes and soften the blow. Effectively using the water and heat in the piping as a buffer against the initial cold-water startup infusion.

    Three parameters are relevant here:

    P12: Pump Cycle Interval time- The amount of time the pump will run when a recirculation is called for. This was originally set to five minutes by my installer because that is how long it took warm water to get to my farthest fixture. At this setting I was getting a cold-water sandwich. I increased this to six minutes and saw a marked improvement.

    Why? My theory: five minutes got water to the farthest fixture but did not fill up all the returning cold line to the NPE. My shower has a temperature regulator. It draws on both the hot and cold lines to maintain its set temp. If there is already warm water in the cold system, it will pull hot less quickly from the hot system. My thinking is that the cold-water rush at startup will have more time to warm up in the pipes before it hits me. I have only now experienced “warm water sandwiches” but not cold.

    P14: Return line sampling.: I reduced this from default of 30 minutes to 15. My thinking that with more frequent sampling it would pull more warm water into the pipes and keep my ‘Pipe Buffer” hotter. I was concerned that with longer sampling intervals the water in the pipes would cool down more.

    P 15: Recirculation differential temperature: I interpret this as the difference between set temp and the return water temp that will turn initiate a recirculation cycle. The default is 9 F. I have set mine to 5F. I am not sure this can make any difference in a cold-water recirculation line set up because the Navicirc valve closes at 95 degrees F. it may be a more relevant adjustment for those with a dedicated hot water line.

    P16: This is only relevant if you are using the hot button and allows on to determine the recirculation

    time needed to your farthest fixture.

    For the Navilink and recirculation to work:

    P01 must be set to your type of device

    P17 must be on for thermal bypass

    P18 must be on to allow communication with the Navilink.

    I have not adjusted any other parameters as they do not affect recirculation to my knowledge.

    In the unit dip switches and valves must also be set correctly if you are using external recirculation. This is listed in their most recent technical bulletins and should be set up by your installer.

    Final thoughts:

    It has been my impression That the Navicirc works better than the Grundfos valve.

    Endless hot water has been fantastic.

    I added piping to an outdoor hose bib that I can be switched to hot water. I use it to refill my hot tub after cleaning and to fill up my pool at the beginning of a season. Extravagant yes, but the water would be heated regardless and this way it is almost instantaneous.

    I can’t say enough good things about the “Tankless Concepts” the company who did my install. Technical bulletins, the app and other things have changed even since my install and they have been amazingly responsive to my questions.


    Navien has done some recent app updates;

    I believe they have fixed the inability to register with IOS 13, but if not, you can register with a device using an older IOS if you have one.

    There has been an issue with schedules not changing automatically over daylight saving time. This may have been fixed but I won’t know until clocks change again.

    I have asked them to create an app based hot button that does not preclude a schedule as well.

    I have asked them to correctly label the enable/ disable buttons.

    If my thinking is flawed here or if anyone has any helpful suggestions please let me know. I hope this has been helpful.
     
  2. Eric The Red

    Eric The Red New Member

    Joined:
    May 21, 2020
    Location:
    Texas
    I just got off the phone with a "Senior" support specialist. I too have the NPE-240A, and this is what was explained to me.
    1. When its just the water heater there is a 30 minute/9 degree re-circulation default set up
    2. Connecting a Hot Button or a Navilink controller to the tankless water heater disables this default because it is assumed that when you hook a Hot Button up you will only want it recirculating when you engage it to do so manually, and when you hook up a NaviLink that you will want to have schedules set up. If you have a hot button and a Navilink hooked up you get the option of one or the other in the app. not both.
    3. This means that when the schedule is disabled it will NOT heat/recirculate.
    4. It means that when outside of the schedule parameters it will NOT heat/recirculate.

    I set my schedule for 7AM when I wake up to 10PM when Everyone would no longer take showers. From what I was told this means it will not run/recirculate overnight from 10:01PM to 6:59AM because of this schedule.

    5. So having found this out, it would seem that the only way to engage a "hot button workaround" would be to enable the schedule...have it figure out/sense the reservoir tank is cold and begin heating the reservoir tank and therefore initiating a re-circulation. There is not a workaround if you have the schedule enabled; disabling it does not initiate a re-circulation.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. dradam

    dradam Member

    Joined:
    Sep 21, 2008
    Location:
    Washington, DC
    If the hot button is not engaged, or a schedule is not specified and enabled in the app then the water heater simply will not re-circulate. Quote

    Have you tried creating a schedule but then disabling the schedule? With a specified schedule if I then disable the schedule my unit will run 24/7 recirc/heat.

    Is your hot button circuit board still installed? Mine is not. It can be easily removed.

    5. So having found this out, it would seem that the only way to engage a "hot button workaround" would be to enable the schedule...have it figure out/sense the reservoir tank is cold and begin heating the reservoir tank and therefore initiating a re-circulation. There is not a workaround if you have the schedule enabled; disabling it does not initiate a re-circulation.[/QUOTE]

    With Navilink installed and communicating (no hot button board installed) and my scheduled program "disabled" my unit recirculates and heats 24/7 as though it were a regular heater as you have shown above 30 min /9 degrees . When my programmed schedule is enabled(working) and I want to take a shower "off" schedule disabling the programmed schedule will initiate unit recirculation and heat if the temp has dropped- hence the workaround. This does indeeed work for me. You must then hit enable again to go back to your schedule or the 30 min 9 degree recirculation will apply 24/7. If this is not your experience perhaps the firmware has changed since my install about 3 years ago. Or perhaps if your hot button circuit board is installed it may have an effect. Be sure your Parameters and dip switches are set correctly.

    To test this ----while the schedule is enabled (and no hot button installed), but you are off schedule go to the unit and then hit disable on the app. If yours works like mine you will see the symbol for recirculation start within moments.

    Obviously the best option would be for Navien to create an app based Hot Button (no additional circuit board) which can be used in conjunction with the scheduler. Despite multiple posts and e-mails they have not done it. That said adding a "D" to the words enable and disabled should be an easy software fix. I ditched and removed the hot button circuit board early on because it did not allow the app to set a schedule. It was one or the other as you have noted. I never tested the "workaround" with the hot button board installed.

    I set my schedule for 7AM when I wake up to 10PM when Everyone would no longer take showers. From what I was told this means it will not run/recirculate overnight from 10:01PM to 6:59AM because of this schedule Quote.

    What you say here is correct-- I hope you know that you can set multiple schedules in one day- such as showers from 7-10 am and 7-pm to 10pm. The unit will not heat or recirculate between schedules(unless you disable the schedule)

    Best wishes.
     
  5. ASB

    ASB New Member

    Joined:
    Nov 17, 2020
    Location:
    CA
    With Navilink installed and communicating (no hot button board installed) and my scheduled program "disabled" my unit recirculates and heats 24/7 as though it were a regular heater as you have shown above 30 min /9 degrees . When my programmed schedule is enabled(working) and I want to take a shower "off" schedule disabling the programmed schedule will initiate unit recirculation and heat if the temp has dropped- hence the workaround. This does indeeed work for me. You must then hit enable again to go back to your schedule or the 30 min 9 degree recirculation will apply 24/7. If this is not your experience perhaps the firmware has changed since my install about 3 years ago. Or perhaps if your hot button circuit board is installed it may have an effect. Be sure your Parameters and dip switches are set correctly.

    To test this ----while the schedule is enabled (and no hot button installed), but you are off schedule go to the unit and then hit disable on the app. If yours works like mine you will see the symbol for recirculation start within moments.

    Obviously the best option would be for Navien to create an app based Hot Button (no additional circuit board) which can be used in conjunction with the scheduler. Despite multiple posts and e-mails they have not done it. That said adding a "D" to the words enable and disabled should be an easy software fix. I ditched and removed the hot button circuit board early on because it did not allow the app to set a schedule. It was one or the other as you have noted. I never tested the "workaround" with the hot button board installed.

    I set my schedule for 7AM when I wake up to 10PM when Everyone would no longer take showers. From what I was told this means it will not run/recirculate overnight from 10:01PM to 6:59AM because of this schedule Quote.

    What you say here is correct-- I hope you know that you can set multiple schedules in one day- such as showers from 7-10 am and 7-pm to 10pm. The unit will not heat or recirculate between schedules(unless you disable the schedule)

    Best wishes.[/QUOTE]

    Hi. Thank you for posting all this info. I also have a Navien NPE 240A that is approx 4 years old in a new home I purchased. The home has a hot water recirculation line. I've contacted Navien support and also had the highest rated tankless company in the area service and check the unit, but can't seem to get a consistent answer regarding the correct/best recirc settings for this unit. Hoping your experience can help me get this right.

    I currently have dip switches 1 and 2 "on" (up) - supposedly to take advantage of the "intelligent pre-heating" and the valve set to 6 o'clock (external). As far as I know, all parameters are set to default. My experience is similar to the issue in your original post in that after the water sits in the lines without demand for a couple hours or so, it takes nearly 2 minutes to get to warm and then another 30 secs or so to get to hot. Not happy. Once a fixture is run and the loop is hot, it's hot at any fixture. I'm used to my other homes that have had an external pump and sidearm tank with a ready supply of hot so this has been a major fail.

    Your post leads me to believe my settings for dip switches and parameters are outdated/wrong. Based on above, what do you recommend based on what you've learned? Thanks very much.
     
  6. spacecowboy

    spacecowboy New Member

    Joined:
    Nov 18, 2020
    Location:
    wild west
    Having just run my own recirc lines and installing an NPE240A I can tell you that you don’t want intelligent preheat.

    The intelligent preheat time watches when heat is called for for about a week and only recircs at that time. If your schedule is not the exact same daily, the system will alway be ‘learning’ and never recirc.

    You will be much happier flipping dip switch 1 off and leaving 2 on and keeping the 2 way valve closed (ext at 6 o clock) to put it in external recirc mode. It will sample the line every 30 minutes and heat the loop if its 9 degrees or more colder than the set temp. If you’re loop is set up right, you’ll have near instant hot water at the expense of burning gas.

    If you want the best of both worlds, get either the navilink or NR20DU remote controller so you can schedule times when you want it to recirc or not.

    I’m still running the numbers to figure out gas usage that recirc for my loop eats before deciding on nothing vs insulate the lines vs controller vs both.

    SC
     
  7. dradam

    dradam Member

    Joined:
    Sep 21, 2008
    Location:
    Washington, DC
    I agree with Spacecowboy-- The information I have refers to external recirculation with cold water line return, but I expect the settings would be the same with a dedicated return line. dip one off, dip 2 on, everything else off (down is off)

    I can send a copy of the Bulletin -- but I can't seem to uplad it here I anyone messages me.
     
  8. dradam

    dradam Member

    Joined:
    Sep 21, 2008
    Location:
    Washington, DC
    Here is the parameter list
     

    Attached Files:

  9. Michael Reily

    Michael Reily New Member

    Joined:
    Sunday
    Location:
    Grass Lake, Michigan
    I have been looking for this for a while, thanks for posting it. Is there a link that I can find this parameter table at? The resolution of the image is not high enough to easily read.
     
  10. Michael Reily

    Michael Reily New Member

    Joined:
    Sunday
    Location:
    Grass Lake, Michigan
    Hello all. I have had my professionally installed NPE-240A for about 8 months now and like it, but do experience longer times to get hot water to all the taps. Today I opened the front panel and saw that all the dip switches were set to off. Am I correct in assuming this means that the internal loop and buffer tank only heat up when there is there is demand for hot water (i.e. a faucet is open) and no recirculation is occuring? From what I have read, I need to set SW1 to on to enable the internal loop recirculation. I expect that would have some positive effect on the time to deliver hot water, even if it is small. The unit is in on one side of our basement and the kitchen is on the far side of the house on the first floor. Eventually, I want to run a return line from the kitchen area back to the hot water heater and that should significantly reduce the delivery time, since all the faucets feed off the line that leads to the kitchen.
     
  11. Bannerman

    Bannerman Well-Known Member

    Joined:
    Mar 19, 2014
    Location:
    Ontario, Canada
Similar Threads: Navien Npe240a-
Forum Title Date
Tankless Water Heater Forum Navien NHB-150 LOOK! Thursday at 12:19 PM
Tankless Water Heater Forum Flushing a Navien CH180 Monday at 2:57 PM
Tankless Water Heater Forum Navien Internal Circulation Pump Pipe Noise Nov 20, 2020
Tankless Water Heater Forum Navien 240A slow hot water Nov 16, 2020
Tankless Water Heater Forum Navien 240S On demand hot water...in principle Nov 13, 2020

Share This Page