This probably goes without saying, but I'm posting it to warn people of the fatal mistake I almost made.
Backstory: I'm moving a washing machine plug as part of a remodel. On the main supply panel, the builder had labeled one 20 amp circuit "washer". I have the wall open, so I could see the supply line dropping down from the attic, going into the plug receptacle. I could also see a wire going out to a receptacle that serves the fridge on the other side of the wall. I used a plug in night light as an interim tester (I'm still alive because I didn't rely on it) and checked both outlets, and the light lit up. I then killed the breaker marked "washer" and checked again; the light didn't work on either outlet.
I *assumed* the "washer" circuit supplied those two outlets. I then pulled the outlet for the washer a bit out of its box (carefully, as if it was live) and checked live-to-ground. I found 120v with the breaker off. Had I not done the second check, I'd be a crispy critter.
Turns out, here's how it was wired. The romex coming down from the attic is 4 core. 2 live wires in it, on two different circuits. One, NOT THE ONE MARKED WASHER, supplies the washing machine outlet. The other supplies the fridge outlet and that's the one marked "washer". The washer outlet was backstabbed (12 gauge wire right into the back, not the screw port) and the neutral was a bit loose (hence my plug in light didn't work the second time).
Had I not checked twice, that combination of a mislabeled breaker plus the intermittent connection would have had me handling live wires thinking they were off. I consider myself lucky to be alive.
So, don't ever trust a breaker label to be what it says, and always double check that the power is actually off, in every circuit within a receptacle box (don't assume there's just one circuit feeding it).
Backstory: I'm moving a washing machine plug as part of a remodel. On the main supply panel, the builder had labeled one 20 amp circuit "washer". I have the wall open, so I could see the supply line dropping down from the attic, going into the plug receptacle. I could also see a wire going out to a receptacle that serves the fridge on the other side of the wall. I used a plug in night light as an interim tester (I'm still alive because I didn't rely on it) and checked both outlets, and the light lit up. I then killed the breaker marked "washer" and checked again; the light didn't work on either outlet.
I *assumed* the "washer" circuit supplied those two outlets. I then pulled the outlet for the washer a bit out of its box (carefully, as if it was live) and checked live-to-ground. I found 120v with the breaker off. Had I not done the second check, I'd be a crispy critter.
Turns out, here's how it was wired. The romex coming down from the attic is 4 core. 2 live wires in it, on two different circuits. One, NOT THE ONE MARKED WASHER, supplies the washing machine outlet. The other supplies the fridge outlet and that's the one marked "washer". The washer outlet was backstabbed (12 gauge wire right into the back, not the screw port) and the neutral was a bit loose (hence my plug in light didn't work the second time).
Had I not checked twice, that combination of a mislabeled breaker plus the intermittent connection would have had me handling live wires thinking they were off. I consider myself lucky to be alive.
So, don't ever trust a breaker label to be what it says, and always double check that the power is actually off, in every circuit within a receptacle box (don't assume there's just one circuit feeding it).