Does my PRV setup need a backflow preventer?

Users who are viewing this thread

TCP

Member
Messages
43
Reaction score
3
Points
8
Location
New York
Hey looking to install a PRV in my home but not sure if I need a backflow preventer. I get around 80-90 psi street pressure coming into the home. Looking to put in a PRV and drop it to around 50-60psi. However, when the sprinklers go off it drops to around 60psi coming into the house (had a gauge on a hose bib). So if I set the PRV at 50 lets say would I need to the BFP? Basically my question is if the house pressure is 10psi or less, greater than line pressure when the sprinklers are running will the BFP be necessary? I have a BFP on the sprinkler side but thats a separate branch off the main. Right now my expansion from my hot water heater goes back to the street but I did install an expansion tank when I put in my new hw heater for this future install. Looking to put in a Watts 25aub-z3 PRV.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
Code still requires the backflow preventer on your sprinkler system. Some people tap off for that prior to the PRV to provide maximum pressure to the sprinklers. Adding a PRV does entail adding an expansion tank in the house as well.
 

TCP

Member
Messages
43
Reaction score
3
Points
8
Location
New York
Yes I have the expansion tank already installed. So will I need a BFP for the house domestic line with the PRV?
 