Is it possible to use a combo wye to catch a tub drain line like below? I am getting conflicting information elsewhere. Or should the 2" line tie into the 4" sewer line downstream of the toilet?

1694890201143.png
 

wwhitney

In the Trades
Messages
6,572
Reaction score
1,848
Points
113
Location
Berkeley, CA
Presume the tub is vented already. I think your question corresponds to the discussion in this thread: https://terrylove.com/forums/index.php?threads/is-this-wet-vent-of-a-toilet-ok-theoretical.89201/
But pay attention to post #31 of that thread.

Looks like Florida has adopted the plumbing portions of the IRC. So if your project is subject to the IRC, the configuration in the OP is not allowed. If it's outside the scope of the IRC (generally one and two family dwellings, if Florida hasn't amended the scoping sections in Chapter 1), then the configuration is allowed under the IPC.


Cheers, Wayne
 

Wernher

New Member
Messages
6
Reaction score
0
Points
1
Location
Florida
Yes that thread helps. Maybe this will help for context. I have read that there is concern with waste getting stuck in the back side of the WYE if installed in this manor and then there are concerns with venting. Maybe I should just move the main line over and come in to it horizontally rather than dropping over the top of it?
1694895449153.png


1694895515191.png
 

Reach4

Well-Known Member
Messages
38,921
Reaction score
4,447
Points
113
Location
IL
What is WB? Is that Wash Basin (lavatory)? Oh,,, maybe wet bar. That might present a problem.
 

Jeff H Young

In the Trades
Messages
8,991
Reaction score
2,249
Points
113
Location
92346
Laundry and tub Id wye off down stream of w/c , Wc would not be a combi just 90 the Tub and Wash machine I would not wet vent .
 

Jeff H Young

In the Trades
Messages
8,991
Reaction score
2,249
Points
113
Location
92346
Only thing is the w/m cant be vent on the tub like that what about a seperat vent in wall for both and tie vent above the box or attic?
 